Also doesn't have to be solid, can be stranded and insulated if you like.
Can I drill a small hole at the edge of my foundation and run my solid 6 ga ground wire out that way
For ground rods, anything bigger than #6 is just wasting money.
Playing devils advocate here, but, can you cite me the article number that requires the wire to be continuous from rod to rod, for example if I've got 2 pieces of wire that won't be long enough to go panel rod rod then why can't I go panel to rod 1, then panel to rod 2?
Where does it say it has to go panel to rod to rod without a break? And why?
250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system shall be installed as specified in 250.64(A) through (F).
(C) Continuous.
Except as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections
shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression type connectors listed as grounding and bonding equipment or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
(3) Bolted, riveted, or welded connections of structural metal frames of buildings or structures.
(4) Threaded, welded, brazed, soldered or bolted-flange connections of metal water piping
Too late now.....but an Ufer would have solved your problem.