Running power to garage
fishon1213
Hello all. I am getting ready to run power to my newly constructed garage. When I remodeled the house I roughed in 6/3 nm from the main panel to corner of the crawlspace, which is roughly another 8 feet from the garage. I have a 100a subpanel and plan on a 60a breaker.
I plan to splice the 6/3 nm to thwn 6,6,6,10 in a metal junction box in the crawlspace, connecting both grounds to the box and using split bolt connections for the conductors. I will use a cable clamp on the nm and a male end with bushings to 1" schedule 80 for the thwn. I will run the thwn/sch80 through the foundation above grade to an LB, then 12" deep to a 90, then a 90 up to an LB into the garage. Another LB up to the subpanel with a male end and bushings.
Does this seem legit?
What specific tape for the split bolts?
Would copper crimp splices be better?
Someone suggested exiting the foundation below grade for a cleaner look, seems like a bad idea to me. Opinions???
I do have a building inspector, this is roughly how he suggested doing it except using uf...I don't like uf. I'm sure he won't be getting in the crawlspace so I just want to make sure I'm doing this right.
Sent from my E6782 using Tapatalk
dirtbikingdad
Are you running 6/3 w/ground? Because you are going to a sub-panel you should have a ground running back to the main panel. The neutral and ground bus connection, if it has one, should be lifted in the sub-panel.
Bert_
NW Iowa
Sounds like a good plan, make sure you use a big enough box for your splice. 6x6x4 would be a nice size, overkill but more room is nice.
Crimps are definitely better but then you need the tool to crimp them. Split bolts will be fine, they also make insulated connectors that would work well for this. A polaris IT-4 would be about right, they can be a little spend-y though.
F
fishon1213
Yes, 6/3 w/ground. And yes on bonded at main but not at sub.
F
fishon1213
Thank you all for the input. I plan to tackle this next week. I've got a lot of irons in the fire. I will take pics and post.
F
fishon1213
I'm finally getting moving on this. Now I just have to do the crawlspace junction box and connect to the main panel.
pattenp
Virginia - USA
I assume you know you need grounding rods at the garage? Also since you used a main lug panel you are limited to 6 breaker circuits by not having a main disconnect at the garage even though the panel will allow up to 12 circuits with the use of tandem breakers.
F
fishon1213
I was under the assumption that I didn't need ground rods but after a bit of reading you are correct. So..two 1/2''x8' copper clad ground rods 6' apart with #6 solid copper ran through 1/2 sch80 connected to my ground bus. Sound legit?
Thanks for the info btw.
pattenp
Virginia - USA
Correct. The 1/2" conduit is not required unless the #6 wire is installed in a location where it may be damaged.
F
fishon1213
Well I did my crawlspace work tonight, splicing 6/3 romex to 6 gauge thwn with 10 gauge ground. I should have used a bigger box and mounted it sideways, other than that and spilling my beer multiple times it went well. Questions...comments...keep in mind I'm not a professional.
F
fishon1213
Did you ground the metal junction box?
Yes, I twisted the grounds and secured them between two fender washers tightened with the ground screw...which I forgot to paint green.