Running power to garage

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
Hello all. I am getting ready to run power to my newly constructed garage. When I remodeled the house I roughed in 6/3 nm from the main panel to corner of the crawlspace, which is roughly another 8 feet from the garage. I have a 100a subpanel and plan on a 60a breaker.

I plan to splice the 6/3 nm to thwn 6,6,6,10 in a metal junction box in the crawlspace, connecting both grounds to the box and using split bolt connections for the conductors. I will use a cable clamp on the nm and a male end with bushings to 1" schedule 80 for the thwn. I will run the thwn/sch80 through the foundation above grade to an LB, then 12" deep to a 90, then a 90 up to an LB into the garage. Another LB up to the subpanel with a male end and bushings.

Does this seem legit?
What specific tape for the split bolts?
Would copper crimp splices be better?
Someone suggested exiting the foundation below grade for a cleaner look, seems like a bad idea to me. Opinions???

I do have a building inspector, this is roughly how he suggested doing it except using uf...I don't like uf. I'm sure he won't be getting in the crawlspace so I just want to make sure I'm doing this right.

Sent from my E6782 using Tapatalk
 
To avoid these ads, REGISTER NOW!

dirtbikingdad

Member
Joined
Mar 26, 2015
Messages
12
Are you running 6/3 w/ground? Because you are going to a sub-panel you should have a ground running back to the main panel. The neutral and ground bus connection, if it has one, should be lifted in the sub-panel.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,732
Location
NW Iowa
Sounds like a good plan, make sure you use a big enough box for your splice. 6x6x4 would be a nice size, overkill but more room is nice.

Crimps are definitely better but then you need the tool to crimp them. Split bolts will be fine, they also make insulated connectors that would work well for this. A polaris IT-4 would be about right, they can be a little spend-y though.
 
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
Are you running 6/3 w/ground? Because you are going to a sub-panel you should have a ground running back to the main panel. The neutral and ground bus connection, if it has one, should be lifted in the sub-panel.
Yes, 6/3 w/ground. And yes on bonded at main but not at sub.

Sent from my E6782 using Tapatalk
 
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
Thank you all for the input. I plan to tackle this next week. I've got a lot of irons in the fire. I will take pics and post.

Sent from my E6782 using Tapatalk
 
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
I'm finally getting moving on this. Now I just have to do the crawlspace junction box and connect to the main panel.
35ac48cee129340d72830171344af07b.jpg
18bd8f5041f274bf2cc3c0bbffad4b92.jpg
e4d6b772a005cff8c9065925a8aac271.jpg
0acfc7309a9e8f610cadbaa4235ada59.jpg
5b403f40bba15799adada933e23f5473.jpg
ea915cc0c6bddf5ec5af09cd2a8570ce.jpg
091fa8874b2fcf513d2abbddc1acd81f.jpg
161fbed0ddf3ac0df70e7655d7cce0d5.jpg
df3003adf7ccaeda73d6381f806f5b34.jpg


Sent from my E6782 using Tapatalk
 

Attachments

  • e4d6b772a005cff8c9065925a8aac271.jpg
    e4d6b772a005cff8c9065925a8aac271.jpg
    66.6 KB · Views: 0

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I assume you know you need grounding rods at the garage? Also since you used a main lug panel you are limited to 6 breaker circuits by not having a main disconnect at the garage even though the panel will allow up to 12 circuits with the use of tandem breakers.
 
To avoid these ads, REGISTER NOW!
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
I assume you know you need grounding rods at the garage? Also since you used a main lug panel you are limited to 6 breaker circuits by not having a main disconnect at the garage even though the panel will allow up to 12 circuits with the use of tandem breakers.
I was under the assumption that I didn't need ground rods but after a bit of reading you are correct. So..two 1/2''x8' copper clad ground rods 6' apart with #6 solid copper ran through 1/2 sch80 connected to my ground bus. Sound legit?
Thanks for the info btw.

Sent from my E6782 using Tapatalk
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I was under the assumption that I didn't need ground rods but after a bit of reading you are correct. So..two 1/2''x8' copper clad ground rods 6' apart with #6 solid copper ran through 1/2 sch80 connected to my ground bus. Sound legit?
Thanks for the info btw.

Sent from my E6782 using Tapatalk

Correct. The 1/2" conduit is not required unless the #6 wire is installed in a location where it may be damaged.
 
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
Well I did my crawlspace work tonight, splicing 6/3 romex to 6 gauge thwn with 10 gauge ground. I should have used a bigger box and mounted it sideways, other than that and spilling my beer multiple times it went well. Questions...comments...keep in mind I'm not a professional.
4a88154a33ddf7a0c172a777ada87344.jpg
ba1cd7ad84ef7cbdd429db81df546260.jpg
3914975fc3abdcb22051df097c514a11.jpg
55ff1b03cab6f7bbb0ecc2569312654b.jpg
b797c130aa891d794d96f2da5137e193.jpg
4c6e854510ff0ae75dc678eea175447d.jpg


Sent from my E6782 using Tapatalk
 
OP
F

fishon1213

Active member
Joined
Mar 15, 2017
Messages
26
Did you ground the metal junction box?
Yes, I twisted the grounds and secured them between two fender washers tightened with the ground screw...which I forgot to paint green.

Sent from my E6782 using Tapatalk
 