So... I am in process of installing a 100 amp sub panel in my detached garage (breakered at 90 amps). I am using 2-2-2-4 MHF from the house to the garage. I am direct burying the MHF because my soil is sand and clay, no rocks within MILES. Inspector said I have to have schedule 80 conduit from the soil to the building. Lowe's only carries schedule 40, WTF?! Where can I find 1 1/2" schedule 80 PVC conduit? I swear this should be simple.
 
To avoid these ads, REGISTER NOW!

Mr_fixit

Well-known member
Joined
May 24, 2008
Messages
1,221
Location
Rustylvania
That inspector seems clueless. mY MISTAKE, I MIGHT BE THE CLUELESS ONE HERE.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
Last edited:

Muzzy

Well-known member
Joined
Jun 20, 2015
Messages
335
Location
Northeast PA
I think its fine, but I'm not your inspector or even an electrician.

I were doing the work at my house I would drill out the knockout in the back that you want to use to 2" and stick with that size all the way through.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,590
Location
Fullerton, CA
I were doing the work at my house I would drill out the knockout in the back that you want to use to 2" and stick with that size all the way through.

A 2" chassis punch costs $50+ and it's a horrible excuse just to save a trip to an actual Electrical Supply.
 

Muzzy

Well-known member
Joined
Jun 20, 2015
Messages
335
Location
Northeast PA
A 2" chassis punch costs $50+ and it's a horrible excuse just to save a trip to an actual Electrical Supply.

Yeah, but I already have a 2 1/2" hole saw that would work just fine. I agree that a supply house would be a better option for the OP to get exactly what he needs instead of what the nearest hardware store happens to have on hand.
 

SGKent

Banned
Joined
Feb 12, 2010
Messages
1,959
Location
Citrus Heights CA
related but not related. My house was built in 1979. Some of the underground are starting to fail. Direct buried. That will mean when they go to replace it they will have to cut concrete driveways, sidewalks in the landscape, etc.. With conduit they could just pull the old out and the new in. Use conduit. You'll save yourself a lot of headaches later on.
 

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,822
Location
(rural) Maryland
related but not related. My house was built in 1979. Some of the underground are starting to fail. Direct buried. That will mean when they go to replace it they will have to cut concrete driveways, sidewalks in the landscape, etc.. With conduit they could just pull the old out and the new in. Use conduit. You'll save yourself a lot of headaches later on.

Or they just directional bore it and are done the job in an hour without tearing up your lawn or concrete...
 

SGKent

Banned
Joined
Feb 12, 2010
Messages
1,959
Location
Citrus Heights CA
Or they just directional bore it and are done the job in an hour without tearing up your lawn or concrete...

There are gas lines and telephone lines in the same area. Also they still have to bust out concrete adjacent to the house to get down under the foundation to the entry point. I had a long talk with the engineers and crew when they were troubleshooting wires shorting to ground in the vault out front.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
Why wouldn't you just call the electrical supply house and get what you need?

I did today. My hope was someone had a magical answer I could have gotten this done this past weekend. On the plus side, schedule 80 at the supply house was cheaper than schedule 40 at Lowe's.
 