Shop panel upgrade

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Please be gentle lol. Just a average diy guy.

when I bought the house the shop was already here. The electric service was poor at best. I made a decision to have a new meter set due to the distance to my house and the huge amount of rock I have. My electric companies transformer is literally 20 feet from the shop. I hung a new 200 amp meter/main disconnect box with feed through lugs. It has 4 spaces. Used them for air compressor and R/v outlet. Fed through to my new panel on opposite side of the wall. Reconnected my circuits with a ton of leftover space if/when I need it. Any constructive criticism is welcomed.
 

Attachments

  • B0ED609D-3298-402E-80C7-6AD4F830AFD8.jpeg
    B0ED609D-3298-402E-80C7-6AD4F830AFD8.jpeg
    207.1 KB · Views: 100
  • 7FE5C861-2302-4546-B680-7B1F0D1B0EEC.jpeg
    7FE5C861-2302-4546-B680-7B1F0D1B0EEC.jpeg
    178.3 KB · Views: 84
  • 767B709F-67A4-4B38-9683-30FC513A71A3.jpeg
    767B709F-67A4-4B38-9683-30FC513A71A3.jpeg
    290 KB · Views: 71
  • 1BC20A61-A755-4687-9CAC-87DAFA70C4CA.jpeg
    1BC20A61-A755-4687-9CAC-87DAFA70C4CA.jpeg
    200.5 KB · Views: 78
  • 78119012-CEF4-4E44-AE79-BA1931EC45E0.jpeg
    78119012-CEF4-4E44-AE79-BA1931EC45E0.jpeg
    263 KB · Views: 84
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
Looks like you terminated neutral and ground onto the same bar in the subpanel

This is a big no no

Ground wire needs to go to its own bar and the neutral bar(s) needs to be isolated by removing the green bonding screw.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
You need to install a ground bar to the metal can of the panel, remove the ground from the lug that it is connected to now and connected it to the new ground bar. All the branch circuit grounds need to be removed from the neutral buss and extended to the new ground bar.

Neutrals and grounds can not be tied together in a sub panel.

I only see one ground rod also. You should have a grounding electrode and a grounding electrode conductor in the meter/main
 
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Looks like you terminated neutral and ground onto the same bar in the subpanel

This is a big no no

Ground wire needs to go to its own bar and the neutral bar(s) needs to be isolated by removing the green bonding screw.
I questioned this with my "help". I was told this wasn't technically a sub panel so separate wasn't required. I read it and understood it as you do but took the bad advice. I can correct it. What device to you prefer to extend my ground wires ?
 
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
You need to install a ground bar to the metal can of the panel, remove the ground from the lug that it is connected to now and connected it to the new ground bar. All the branch circuit grounds need to be removed from the neutral buss and extended to the new ground bar.

Neutrals and grounds can not be tied together in a sub panel.

I only see one ground rod also. You should have a grounding electrode and a grounding electrode conductor in the meter/main
I questioned this with my "help". I was told this wasn't technically a sub panel so separate wasn't required. I read it and understood it as you do but took the bad advice. I can correct it. What device to you prefer to extend my ground wires ?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I questioned this with my "help". I was told this wasn't technically a sub panel so separate wasn't required. I read it and understood it as you do but took the bad advice. I can correct it. What device to you prefer to extend my ground wires ?
It is a sub panel. Your meter/ main is your main panel. It has your first means of disconnect. You did right by the 4-wire feed to your sub panel. There should be spots to attach ground bars in the panel. That is a Square D Homeline panel, just get ground bars made for that panel and the holes will line up to mount them. I like putting one on each side. If you have to extend the grounds on the branch circuits, i just use wire nuts and the same size wire. If you want to extend the main equipment ground to the ground bars, you just have to attach it to one, you can use a split bolt to do this. Make sure it is the same size wire also. You could also just add a lug down by the equipment ground and not extend it.

I still would think you need another ground rod. If your utility has a service hand book, it would be in there. what size is that conduit and wires feeding the sub panel?


Also, here is a thread on extending ground wires

 
Last edited:
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
It is a sub panel. Your meter/ main is your main panel. It has your first means of disconnect. You did right by the 4-wire feed to your sub panel. There should be spots to attach ground bars in the panel. That is a Square D Homeline panel, just get ground bars made for that panel and the holes will line up to mount them. I like putting one on each side. If you have to extend the grounds on the branch circuits, i just use wire nuts and the same size wire. If you want to extend the main equipment ground to the ground bars, you just have to attach it to one, you can use a split bolt to do this. Make sure it is the same size wire also. You could also just add a lug down by the equipment ground and not extend it.

I still would think you need another ground rod. If your utility has a service hand book, it would be in there. what size is that conduit and wires feeding the sub panel?


Also, here is a thread on extending ground wires

Thank you. I will get it corrected. I do have two grounds, the second connection is under the dirt. Conduit is 1&1/2. Wish it was 2" but I already had it and was trying to save a couple $
 
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Thank you. I will get it corrected. I do have two grounds, the second connection is under the dirt. Conduit is 1&1/2. Wish it was 2" but I already had it and was trying to save a couple $
The wire feeding the sub is 2/0 with a 4 gauge ground wire
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,813
Location
Southern Oregon
Your RV circuit is using a red with white tape as neutral. Pretty sure that #6 and smaller neutrals must be white/gray and you're not allowed to reidentify them.
 
To avoid these ads, REGISTER NOW!
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
You need to install a ground bar to the metal can of the panel, remove the ground from the lug that it is connected to now and connected it to the new ground bar. All the branch circuit grounds need to be removed from the neutral buss and extended to the new ground bar.

Neutrals and grounds can not be tied together in a sub panel.

I only see one ground rod also. You should have a grounding electrode and a grounding electrode conductor in the meter/main
Ok Terry I think I have it corrected. Here's a couple pics
 

Attachments

  • 8A92847C-A729-42F5-8E78-897414125599.png
    8A92847C-A729-42F5-8E78-897414125599.png
    3.9 MB · Views: 46
  • 1000CE5B-706C-4D3C-B72E-34E593439C46.png
    1000CE5B-706C-4D3C-B72E-34E593439C46.png
    3.5 MB · Views: 50
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Looks like you terminated neutral and ground onto the same bar in the subpanel

This is a big no no

Ground wire needs to go to its own bar and the neutral bar(s) needs to be isolated by removing the green bonding screw.
I think I have it corrected. Pics are dark but I think u can zoom in and see
 

Attachments

  • E5EB6678-DF1E-4CE6-BB90-1593E629575C.png
    E5EB6678-DF1E-4CE6-BB90-1593E629575C.png
    3.9 MB · Views: 51
  • B837B898-B38E-4A9D-AD6F-BE467EEC34EF.png
    B837B898-B38E-4A9D-AD6F-BE467EEC34EF.png
    3.5 MB · Views: 54

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Ok Terry I think I have it corrected. Here's a couple pics
Looks good. Is that splice connector you used dual rated for copper and aluminum. Most of them are. I know you used all copper, just making sure the connector is rated for copper. Other than that you have fixed the problem.
 
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Looks good. Is that splice connector you used dual rated for copper and aluminum. Most of them are. I know you used all copper, just making sure the connector is rated for copper. Other than that you have fixed the problem.
Yes it did say on the package that it was rated for both
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
I questioned this with my "help". I was told this wasn't technically a sub panel so separate wasn't required. I read it and understood it as you do but took the bad advice. I can correct it. What device to you prefer to extend my ground wires ?
Your “helper” was dangerously wrong.

Hopefully theyre not licensed.

See the electrical FAQs sticky for wiring diagrams.
 
OP
O

otef546

Well-known member
Joined
Jan 4, 2009
Messages
54
Your “helper” was dangerously wrong.

Hopefully theyre not licensed.

See the electrical FAQs sticky for wiring diagrams.
Scary thing he is licensed. Thanks for your help. Bad thing I was 90 percent that it was wrong but let myself get convinced otherwise
 