Looking for some advice/help

I am in the process of building my dream shop. 40 x 60 wood frame building with 2 x 6 studs 12’ High walls and gables on each end. Total height is 23’ with the 8/12 pitch Roof.

The problem I’m having is one of the gable ends is bowing out at the top plate. It is bowed outward 3 1/2”. The baseplate and the peak are plumb but the top plate is pushing uutward making the wall have a V shape top to bottom.

I can pull the wall straight with a ratchet strap but keeping it straight is the problem. There are no joist connecting that wall so it’s a long span.

I have thought about bolting a c8x18 to the face of the top plate and studs but I’m not sure if that would also deflect over such a long span.
Thanks for any help or suggestions.
It’s the wall right above the title “floor plan & plumbing layout”
Brian
 

Attachments

  • C3E37C2F-858D-4FFF-A01C-31DB1016A2AF.jpg
    C3E37C2F-858D-4FFF-A01C-31DB1016A2AF.jpg
    19.4 KB · Views: 547
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
The double top plate (iow adding the 2nd top plate) should help handle this if you keep the wall straight as its nailed off. You could potentially also use flat metal strapping in a "V" profile as seen from above, with the vertex near the centerline of the wall. The thin metal would then nail to the bottom chords of the trusses and ideally end at the top plate of the other walls.

See also - Simpson part # CS16 "coiled strap 16 gage"

Imo, bolting on a heavy metal channel is directionally correct but now you are into attaching wood to metal, that's never fast or easy. While it might bolt down quickly, fitting and attaching the endwall truss won't merge with that very fast.
 
Last edited:
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
Matt, thanks for the reply.
The trusses are pitched with the roof, like a cathedral ceiling so they can’t be tied to. The roof is (8/12 ceiling is 6/12) so the top plate can’t be tied to it.
Hand drawing of what’s it’s doing and a pic looking up one of the studs, check out the space between the string line and the stud. String line was pulled corner to corner at the top plate
 

Attachments

  • F08B3E8E-7627-44E6-A318-47E6B4EDAC33.jpg
    F08B3E8E-7627-44E6-A318-47E6B4EDAC33.jpg
    64.4 KB · Views: 368
  • 826A8CE4-39E1-4E9F-AEC1-FCCFA99FC780.jpg
    826A8CE4-39E1-4E9F-AEC1-FCCFA99FC780.jpg
    63.3 KB · Views: 466
Last edited:

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,384
Location
Colorado
Not a fan of the way the end wall was constructed. Face off, tie the upper verticals framing members to the wall studs with dimensional lumber and it will all pull together. You'll end up w/ a thicker wall but that's not all bad.
Excuse the chicken scratches.
Jim
IMG_3148.jpg
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
On a wall that long is going to be hard to build stiff.
I am used to seeing 2x4s from wall to wall at a 45 degree across the corners at the top plate.

I your case you would lose some of the vaulted area in the corners.
But that may be the price you have to pay.
 

like2wheel

Well-known member
Joined
Oct 29, 2014
Messages
1,693
Location
On an as needed basis
Had that problem with my mom's garage when I was young. Solved it by pulling it straight & building a shelf across to keep it stiff. Shelf came in handy.

Don't know if that works for your situation.
 

383

Well-known member
Joined
Aug 14, 2011
Messages
1,230
Location
Harrisonburg, VA
Sawzall 5 1/2" out of the plate and run a 6x6 from the bottom plate to the bottom of the truss. Pull the wall in and nail everything to the post. The building is 40' wide, you could add two 6x6's to the wall and make a huge difference.
 

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
if I'm understanding this correctly you'll never stiffen that wall until you do something like 383 said, you need to cut out that top plate maybe every 4' and run some continuous studs from the bottom plate and tie them to the bottom of the truss.
I had a similar situation where I had a short wall up to the bottom of a end scissor truss and I could not get that wall stiff until I doubled up some 14' 2x4's and made them continuous from the bottom plate up to the bottom of the truss it made a world of difference. This was in a previous house I had.

it's hard to see in the pic but if you look close you can see where the studs are doubled up, the inspector made me put that 10ga plate along the top 2x4 plate which didn't do anything
 

Attachments

  • DSCN3216.jpg
    DSCN3216.jpg
    151.5 KB · Views: 324
Last edited:
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
On a wall that long is going to be hard to build stiff.
I am used to seeing 2x4s from wall to wall at a 45 degree across the corners at the top plate.

I your case you would lose some of the vaulted area in the corners.
But that may be the price you have to pay.

Good idea, I had thought of also using a cable with a turnbuckle as well
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
if I'm understanding this correctly you'll never stiffen that wall until you do something like 383 said, you need to cut out that top plate maybe every 4' and run some continuous studs from the bottom plate and tie them to the bottom of the truss.
I had a similar situation where I had a short wall up to the bottom of a end scissor truss and I could not get that wall stiff until I doubled up some 14' 2x4's and made them continuous from the bottom plate up to the bottom of the truss it made a world of difference. This was in a previous house I had.

it's hard to see in the pic but if you look close you can see where the studs are doubled up, the inspector made me put that 10ga plate along the top 2x4 plate which didn't do anything

I see what y’all are talking about! Makes sense. I’m going going to look at the framing in the morning and see how I might do this.
Thanks
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
Does the outside sheathing break on that double top plate or does it span it ?

I’m not sure, but a good point. With what this frame crew has done.... or not done I wouldn’t be surprised if they didn’t stagger the plywood. They already installed the tyvek wrap and brick ties so I can’t really check.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
You took the easy rout.....and now you are paying the price.

Basically, you built the first part of the wall using all the same length studs....put a plate on top of that....then built up the rest.

In other words, you're depending on that first plate to keep the wall straight....which it is not...

I think you need to cut that first plate and put doublers in there.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado

Very Interesting... thanks Captain!

You would think this would be a code requirement?

attachment.php
 

Attachments

  • Scissor Truss.jpg
    Scissor Truss.jpg
    70 KB · Views: 946
Last edited:

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
Looking for some advice/help

I am in the process of building my dream shop. 40 x 60 wood frame building with 2 x 6 studs 12’ High walls and gables on each end. Total height is 23’ with the 8/12 pitch Roof.

The problem I’m having is one of the gable ends is bowing out at the top plate. It is bowed outward 3 1/2”. The baseplate and the peak are plumb but the top plate is pushing uutward making the wall have a V shape top to bottom.

I can pull the wall straight with a ratchet strap but keeping it straight is the problem. There are no joist connecting that wall so it’s a long span.

I have thought about bolting a c8x18 to the face of the top plate and studs but I’m not sure if that would also deflect over such a long span.
Thanks for any help or suggestions.
It’s the wall right above the title “floor plan & plumbing layout”
Brian

Can you take out the blocking and frame in full height studs? You essentially built a hinge into the wall. Either need continuous member, or a beam behind to remove the hinge. It will be a massive beam to handle the load and deflection.

Other option is to use plywood and attach to the underside of the trusses and the top plate that is their. Essentially creating a diaphragm using plywood.

The details will be in the connections though.
 
To avoid these ads, REGISTER NOW!

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,867
Location
Northern Central Ohio

I believe this is one of the most informative link posted here. Thanks to lakeroadster for bringing a section of it over here.


Notice how the full length studs run all the way to the top ? Laying the exterior sheathing out to span as many studs as possible will help strengthen the wall too.

If the work crew doesn't fix this mistake, than you need to or find somebody that will before any exterior finish goes on.
 

The Tool Tyrant

ALLIANCE MEMBER
Joined
Dec 19, 2011
Messages
2,182
Location
Bonita, Ca. (San Diego)
As others have suggested, best fix at this point would be to cut the plates at the hinge point and run continuous 4x6 or 6x6 posts from the bottom plate to the top plate. Personally, I'd start at the center, installing the posts @ 8'0 O.C. each direction and if that doesn't suffice, add an additional post in between. Finally, run Simpson coil strap at the block line to tie it back together.
Your "framers" should have known better!
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
Great info and that link was awesome. I believe this is gonna be my next course of action.
I’m going to not touch the 2 x 6 top plates and install double 2x4’s and sandwich the studs together.
I think that should work. I think I’m going to do every stud for piece of mind as the cost is not going to be bad at all just a lot of time.
What do y’all think
Thanks again for the advice.
BTW the frame crew quit.
 

Attachments

  • 183EB578-7FD3-4DAC-9136-724FB1D20802.jpg
    183EB578-7FD3-4DAC-9136-724FB1D20802.jpg
    126.5 KB · Views: 145
  • AF451AB8-43D5-4365-A487-0AAC00B8499E.jpg
    AF451AB8-43D5-4365-A487-0AAC00B8499E.jpg
    148 KB · Views: 167
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
This is what I have in mind.
 

Attachments

  • D734C346-FFFD-4348-B931-07A7663AE1A1.jpg
    D734C346-FFFD-4348-B931-07A7663AE1A1.jpg
    98.4 KB · Views: 143
  • A7143DAC-9BDB-400F-B3ED-EF2A23B2849D.jpg
    A7143DAC-9BDB-400F-B3ED-EF2A23B2849D.jpg
    87.3 KB · Views: 130
  • CB62A11A-712B-4B4B-96AA-D9C53F737B3F.jpg
    CB62A11A-712B-4B4B-96AA-D9C53F737B3F.jpg
    83.3 KB · Views: 136

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,319
Location
Ashland, VA
Lots of helpful responses here.

I can't help with specific advice, but I can offer this: talk to your building inspector sooner rather than later. They might have other ideas and if you point out problems they might otherwise miss, they'll be more critical when it comes time to do their inspections. Thats not a bad thing, IMHO.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
What do y’all think

Did you get a permit? Are there inspections?

If the answer is yes an engineer will need to approve the changes and someone will need to revise the drawings and resubmit them to the county / city.

I'd suggest to the engineer that the existing top plate be cut and 2x6's installed on 16" c/l's, sistered to the existing 2's.

And I'd be pushing the engineering firm to do the updates for free... they should have known better.
 
Last edited:
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
Did you get a permit? Are there inspections?

If the answer is yes an engineer will need to approve the changes and someone will need to revise the drawings and resubmit them to the county / city.

I'd suggest to the engineer that the existing top plate be cut and 2x6's installed on 16" c/l's, sistered to the existing 2's.

And I'd be pushing the engineering firm to do the updates for free... they should have known better.

I live in a small town, engineering is not required and the plans as built were approved.
 

Homerr

Well-known member
Joined
Mar 16, 2012
Messages
379
Location
Seattle, WA
This is what I have in mind.

I've been designing and drawing homes for 30 years. This seems woefully inadequate and I think you're overestimating what 2x4's will do.

Keep in mind that you're not just straightening the wall for aesthetics, it should be structurally sound to withstand seismic and, probably more critically, high wind loads. All of us quasi-engineering this is probably a bad idea.

Get an engineer involved for a few hundred bucks. They will probably want everything shored back to eliminate the V and then block the bottom chords of the trusses and possibly plywood the ceiling to create a diaphragm at the ceiling; or they may have a way to diagonally brace the top plates up through the truss webbing to the roof diaphragm; or something like what 383 said at so many feet on center in the gable. If you have no idea what I'm talking about then it really is time to call an engineer.

:beer:
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
I live in a small town, engineering is not required and the plans as built were approved.

You're modifying the construction such that it no longer meets the specified plans that were approved.

Just be aware, if there is ever an issue, your modifications may shift responsibility away from the engineering firm and back on to you.

Whenever there is an issue or failure the first thing that inspectors look for is a deviation from the approved plans.

Just looking out for you. Good luck with your project.
 
Last edited:

RocketScott

Well-known member
Joined
Jul 20, 2016
Messages
262
Location
Lexington, KY
If the top of the truss is good all those flat blocks at the top of the wall are probably pushing the gable out. When you ratchet it back in do you have a bulge in the gable truss at that spot?

I'd start by removing anything in the trusses that connects the gable end to the rest of the trusses then see where it sits.
 

dave_dj1

Well-known member
Joined
Feb 3, 2018
Messages
222
Location
Jackson, NY
One well placed 4x6 in the center should straighten things right up. Maybe add a couple of brackets where you cut the plate for it.
Why did they use a truss and then frame in front of it?
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,092
Location
AZ
This is what I have in mind.



That won't work. You're not understanding how to mitigate the hinge point that splitting the framing at the top plate created. The only way to straighten that wall and maintain it plumb is to do as suggested. Or you could sister it on the inside but you'll lose depth either the entire wall or maybe create three columns.

Good luck.
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
One well placed 4x6 in the center should straighten things right up. Maybe add a couple of brackets where you cut the plate for it.
Why did they use a truss and then frame in front of it?
The 2x4 were added to make the inside wall flush for sheet rock
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
That won't work. You're not understanding how to mitigate the hinge point that splitting the framing at the top plate created. The only way to straighten that wall and maintain it plumb is to do as suggested. Or you could sister it on the inside but you'll lose depth either the entire wall or maybe create three columns.

Good luck.
I thought that was what I was basically drawing out. Studs going from the floor to the truss. I’m just going to sandwich the existing studs between them.
 

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
Great info and that link was awesome. I believe this is gonna be my next course of action.
I’m going to not touch the 2 x 6 top plates and install double 2x4’s and sandwich the studs together.
I think that should work. I think I’m going to do every stud for piece of mind as the cost is not going to be bad at all just a lot of time.
What do y’all think
Thanks again for the advice.
BTW the frame crew quit.

I dont think 2-2x4's is the same as a 2x6, the moment of inertia is off by 2 times, meaning your 2-2x4's will deflect twice as much as the 2x6. You cant count on the 2x6 reall since it has a big gap in it where the plates are at.

Cut out the top plate at each stud and sister 1-2x6 full height to the existing.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,585
Location
Kingsport, TN
2x4's will work beautifully, and are very strong compared with the nothing whatsoever that you have now. My opinion.

Top plates would actually have been adequate had they been straight, but 2x4's from floor to ceiling will be much stronger.
 
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
I dont think 2-2x4's is the same as a 2x6, the moment of inertia is off by 2 times, meaning your 2-2x4's will deflect twice as much as the 2x6. You cant count on the 2x6 reall since it has a big gap in it where the plates are at.

Cut out the top plate at each stud and sister 1-2x6 full height to the existing.

I can’t use a 2x6 all the way to the top as the end gable truss would be in the way. In this picture you can see the 2x6 studs ending at the top plate, and then there is a gable on top of the top plate and a 2x4 wall that goes up behind the gable. The gable will be in the way of running a 2x6 all the way up.
I hope I’m explaining that correctly.
I would rather use 2x6’s but they won’t work/fit the upper wall.
 

Attachments

  • 25565A33-56BA-4A8C-BA73-9B5BD6278414.jpg
    25565A33-56BA-4A8C-BA73-9B5BD6278414.jpg
    126.5 KB · Views: 61
OP
B

BigBri

Well-known member
Joined
Aug 12, 2015
Messages
84
Location
Louisiana
This shows the sizes
 

Attachments

  • C6C7A18D-A2EB-466D-B414-3F461FC83771.jpg
    C6C7A18D-A2EB-466D-B414-3F461FC83771.jpg
    147 KB · Views: 58

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Propose the following to the engineer:

Cut the top plate, beside each (**) vertical stud, making a 1-1/2" wide slot that is 3-1/2" deep. You can use a hand held circular saw for this or a sawzall, or both.

Install a new 2 x 6 top double top plate to the top chord of the gable truss. Where these top plates meet at the ridge use Simpson heavy plate and 3" structural screws. (you can temporarily add 2 x 4's on the top chord of the gable truss to the 1st scissor truss to support the new double top plates.)

Slide a 2 x 6 into the slot and attach it to the existing studs. This 2 x 6 will go from the bottom sill plate all the way to the new top plate at the top of the gable truss.

Attach the top of the new 2 x 6 studs to the new top plate using Simpson angle brackets and structural 1-1/2" screws.

You will loose 1-1/2" of interior space.

(**) The Engineer may allow you to do these on 32" c/l's (every other stud) instead of every stud. You can then use 1-1/2" x 1-1/2" to space out the other studs for your wall sheathing.

This eliminates the "hinge effect".

attachment.php


attachment.php


____________________________________________

And this is why you need to get an engineer involved. None of us know the specific environmental conditions at your location.

One guy says 2 x 4's may not work, one guy says they will work "beautifully". The Engineer will evaluate the design based on your specific site conditions, environmental conditions and zoning requirements.

I dont think 2-2x4's is the same as a 2x6, the moment of inertia is off by 2 times, meaning your 2-2x4's will deflect twice as much as the 2x6. You cant count on the 2x6 reall since it has a big gap in it where the plates are at.

Cut out the top plate at each stud and sister 1-2x6 full height to the existing.

2x4's will work beautifully, and are very strong compared with the nothing whatsoever that you have now. My opinion.

Top plates would actually have been adequate had they been straight, but 2x4's from floor to ceiling will be much stronger.
 

Attachments

  • BigBri  Saw Cut.jpg
    BigBri Saw Cut.jpg
    130.8 KB · Views: 308
  • BigBri  Saw Cut 1.jpg
    BigBri Saw Cut 1.jpg
    122.9 KB · Views: 307
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom