MKSJ
Active member
If you have the name/picture of the VFD, then some guidance could be provided as to programming.
HY VFD's
PD003 Main Frequency 60.00
PD004 Base Frequency 60.00
PD005 Max Operating Frequency 60.00
PD075 Higher Analog Frequency 60.00
The issue is a VFD is not a 3 phase power source to run electronics and control circuits, the output is PWM and is designed to power motors not electronics. You would need something like a Phase Perfect or a RPC, and the latter will be much less expensive. If using an RPC you need to not use the wild generated leg to power the electronics/transformers, otherwise it may run erratic and damage the semiconductor controls.
HY VFD's
PD003 Main Frequency 60.00
PD004 Base Frequency 60.00
PD005 Max Operating Frequency 60.00
PD075 Higher Analog Frequency 60.00
The issue is a VFD is not a 3 phase power source to run electronics and control circuits, the output is PWM and is designed to power motors not electronics. You would need something like a Phase Perfect or a RPC, and the latter will be much less expensive. If using an RPC you need to not use the wild generated leg to power the electronics/transformers, otherwise it may run erratic and damage the semiconductor controls.