The efficiency of a pressurized system is higher than one with an "open" expansion tank. When the system is sealed and pressurized, the movement of the fluid and the heat is better than having a system that is open to the air. With the ability of the pump to cavitate and create more air in an open, unpressurized system the "open" pvc tube is probably required to remove the large amounts of air.
OK hold it a sec. Cavitation does not "create air". It creates water vapor. Cavitation is caused when the action of the pump makes the pressure in areas of the impeller drop below the vapor pressure of the fluid being pumped. Then the fluid actually
boils, creating a pocket of steam (cold steam!).
Cavitation reduces the efficiency of a pump and this may be enough argument for a pressurized system
if the pump is cavitating. Severe or prolonged cavitation can damage a pump, but unlikely to cause anything more than cosmetic damage in this application. (My car redlines at 9000 RPM, and is often driven in that vicinity to keep it healthy. The water pump is known for cavitation at those speeds and leaves a rough surface in the pump housing.)
But even extreme cavitation is not going to generate anything to go out the vented expansion tank. Once the vapor leaves the immediate area causing the low pressure the steam pocket collapses, leaving nothing behind but noise.
Anyway, I sincerely doubt cavitation is a problem here. But I do wonder if the heater's efficiency isn't increased by pressure by keeping those little boiling hot spots to a minimum?
When the system is closed and pressurized, once the air has been purged from the tubing/system, the heated water will travel in a more efficient manner being pushed through by the pump instead of relying on gravity to feed the pump and or tubing.
You're saying a closed loop is more efficient because of higher pressure at the pump inlet?
That doesn't make a darn bit of difference if the pump isn't sucking air or cavitating.
And there's no guarantee the pump will see higher relative inlet pressure in a closed system.
The reasoning behind adding a glycol substance is not to raise the boiling point, but to keep the lines from freezing if/when the boiler/heat source goes down in the winter or the home owner doesn't start it up soon enough.
That makes sense. And no doubt to keep green goo from making a home in the plumbing too.
YMMV...my advice and experience and $5 will get you a happy meal at McDonalds.
Same here, except my advice and experience and $5 will get you a cup of coffee at Starbroke's!