Simple wiring question...

katomike

New member
Joined
Dec 14, 2011
Messages
3
NEC 300.3 says that all conductors of the same circuit, including grounding and bonding conductors shall be contained in the same raceway, cable, or trench. Is it okay to have 10-2 come out of the panel to a junction box then to another junction box with wiring for outlets coming out of each junction box? I have attached a diagram to hopefully make my question more understandable.

Thanks for your help!
 

Attachments

  • 240V Wiring Diagram.jpg
    240V Wiring Diagram.jpg
    19.2 KB · Views: 127
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You diagram is okay. The intent of the code is for the hot, neutral and ground to remain together in the same cable or conduit. Another issue is for your 240V circuit is if it's greater than 20A then multiple outlets are not allowed by International Residential Building Code. 30A and greater are to be dedicated circuits to one outlet (receptacle). E3702.5 https://codes.iccsafe.org/public/document/code/553/9874212



*
 
Last edited:
OP
K

katomike

New member
Joined
Dec 14, 2011
Messages
3
The 240V circuit will be on a 30A outlet...so I guess that each outlet will need a dedicated circuit. Thanks for your help!!
 
OP
K

katomike

New member
Joined
Dec 14, 2011
Messages
3
Table saw. Also, if I run 10-2 from a 20A breaker can I use 12-2 out of a junction box to outlets?

Thanks!!
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Table saw. Also, if I run 10-2 from a 20A breaker can I use 12-2 out of a junction box to outlets?

Thanks!!

Like Diesel said....why 10-2?

If you are 20A or less....just use the 12-2

If you think there is some chance you may go 30A later, then, yea, run 10-2.

Just remember, you can't daisy chain any 240Vac ckts over 20A. If you have 2 different 240 drops, each has to be it's own breaker and wires.

Personally, even if they were 20A or less, I'd still run separate ckts.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
Like Diesel said....why 10-2?

If you are 20A or less....just use the 12-2

If you think there is some chance you may go 30A later, then, yea, run 10-2.

Just remember, you can't daisy chain any 240Vac ckts over 20A. If you have 2 different 240 drops, each has to be it's own breaker and wires.

Personally, even if they were 20A or less, I'd still run separate ckts.

If OP is under the IBC...otherwise he can since NEC has no prohibition against doing so...

Hi,
How to series a circuit of 220 volt I want to see diagram

Did u mean daisy-chain? All AC outlets are wired parallel....
 