Splicing different gage wire?

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
Ok so without going into crazy detail, I need to splice #10 wire to #2 wire in a junction box. What is the best way to accomplish this?

Sent from my SM-G920W8 using Tapatalk
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,371
Location
Michigan
I see some polaris connectors rated from 1/0 to 14 gauge if you prefer those over a split bolt.
 
OP
J

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
For what purpose are you splicing #10 to #2?
Well it's a bit convoluted, but here goes. Our current house had #2 wire ran underground between my basement and garage. It entered the basement and just ran open air to a fused disconnect and then to my panel. We sold the house and the buyers requested an electrical inspection. I was told I can't have that ran open air in the basement and I need to correct it. So my plan is to cut it off just inside the basement, pull it back outside, feed it into a weather tight plastic junction box attached to the foundation, then remove the fused disconnect inside the house, and run a length of 10/3 grounded Romex from the panel to the outdoor box, then connect the 10 and 2 together in the box. That should make the inspector happy and if the new buyers want more than 30 amps, they can replace the run from the panel to the outdoor box with bigger wire.

Sent from my SM-G920W8 using Tapatalk
 
OP
J

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
Why pull it back ? Feed the #2 directly into the back of a junction box mounted to the basement wall.
The only reason I was going to pull it back was to continue the conduit from underground. It comes up in conduit then the previous owner just slid a sleeve over it and fed it through the concrete.

Sent from my SM-G920W8 using Tapatalk
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I believe you can purchase split bolts that are rated for both copper and aluminum.

Those can be used for either cu to cu or al to al, but not cu to al. Splice/reducers keep the wires from touching each other.

Edit: I forgot the Al/Cu split bolt has a spacer.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
20 or 25 feet, and the #2 doesn't run all the way to the panel, just to a disconnect.

Sent from my SM-G920W8 using Tapatalk

Is the disconnect fused?

And pricing it out 3 sticks of 1 1/4" sch 40 some glue and maybe an LB will cost u about $30 wheres 10/3 NM-b is gonna run you $45-$50 plus staples PLUS the appropriate connector to splice cu to al (addl $20+ ??) and thats IF its not subject to damage.

So you will be spending more money on the hack job you propose vs. doing it right.

Why do u want to go the NM-b route again?
 
OP
J

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
Is the disconnect fused?

And pricing it out 3 sticks of 1 1/4" sch 40 some glue and maybe an LB will cost u about $30 wheres 10/3 NM-b is gonna run you $45-$50 plus staples PLUS the appropriate connector to splice cu to al (addl $20+ ??) and thats IF its not subject to damage.

So you will be spending more money on the hack job you propose vs. doing it right.

Why do u want to go the NM-b route again?
Trying to figure out the easiest way to get this passed inspection and be done with this **** show.

This is what I have now feeding my garage.
3ccd32f85da49f43c57c47fd07f988ea.jpg

The big stuff is run unprotected inside the house, and that old disconnect is in rough shape. It's only being fed with #10 wire as it stands. The inspector needs all that cable in a conduit which I figure is going to be a nightmare since it runs behind a book case and out the wall.

In my mind it just seems easier to cut it back and put it in a box and then run some wire that doesn't have to be in conduit.

Sent from my SM-G920W8 using Tapatalk
 

Attachments

  • 3ccd32f85da49f43c57c47fd07f988ea.jpg
    3ccd32f85da49f43c57c47fd07f988ea.jpg
    76.1 KB · Views: 0

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,110
Location
Modesto, CA
so the old cloth wrapped #10 on the left side of the top of the disconnect comes from your main panel?

And its breakered @ 30a?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Do not use split bolts. Use splice/reducer rated for AL/Cu. Do not connect aluminum and copper directly together.

AL/CU listed split bolts are available, I prefer Polaris type connectors myself.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
AL/CU listed split bolts are available, I prefer Polaris type connectors myself.

Yeah.. I realize that Al/Cu split bolts are available. I had a brain freeze moment. Polaris are nice, I just can't bring myself to pay what they cost.
 