The main panel in my garage (SD QO) feeds a sub panel in my basement via a 125A (Q12125) breaker that looks like this:

I need to add a 220 circuit for a planer but the main panel is completely full. Is there any reason that I can't replace this old behemoth with a standard 125A breaker that only takes 2 slots instead of 4? Any idea why this would need 4 slots? It being 220, it already contacts both bus bars. What is the advantage of bridging both sides of the box?

I need to add a 220 circuit for a planer but the main panel is completely full. Is there any reason that I can't replace this old behemoth with a standard 125A breaker that only takes 2 slots instead of 4? Any idea why this would need 4 slots? It being 220, it already contacts both bus bars. What is the advantage of bridging both sides of the box?