Sub panel help

badams14

Member
Joined
Jul 21, 2015
Messages
22
Any one know what size wire I will need for a 210' run of direct burial to a 100A sub panel? Main 200A panel is in basement, underground to new pole barn from there. Thanks in advance.


Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You can use type RHH/RHW-2/USE wire if doing direct bury and make up your 4 wires if you don't want the assembled MHF cable. As said the closest size of MHF is 2/0, so making up the run from individual wires you should be able find the #1-Cu or #1/0-Al to do so. Remember the EGC can be smaller than the current carrying conductors.
 
OP
B

badams14

Member
Joined
Jul 21, 2015
Messages
22
I have had a few local electricians tell me I should use 1/0 copper on the hot legs, #2 on the neutral and #6 on the ground. Sound right? I do all the work myself but the last thing I want is to do it again because an inspector has a problem with it. Thanks.


Sent from my iPhone using Tapatalk
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
You're getting ahead of yourself.

First, how did you come up with needing a 100 amp panel? What kind of equipment will be in your garage? HVAC?
 
To avoid these ads, REGISTER NOW!
OP
B

badams14

Member
Joined
Jul 21, 2015
Messages
22
HVAC, welder, lathe, drill press and maybe a milling machine. I do not plan on using 100A but I would like the option down the road if necessary.


Sent from my iPhone using Tapatalk
 

davidlee

Well-known member
Joined
Aug 1, 2012
Messages
275
Location
Pensacola, Fl
I ran a 4 wire direct burial aluminum wire number of years ago and it did not hold up well. I then ran copper in conduit and it has lasted. I would not recommend direct burial if something happens there is no fix, just dig it up and replace it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
I have had a few local electricians tell me I should use 1/0 copper on the hot legs, #2 on the neutral and #6 on the ground. Sound right? I do all the work myself but the last thing I want is to do it again because an inspector has a problem with it. Thanks.


Sent from my iPhone using Tapatalk

The 6 AWG grounding conductor would not be in compliance with 250.122(B). as the ungrounded conductors has been increased from the minimum conductor size required for the installation.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,360
Location
SE MI
HVAC, welder, lathe, drill press and maybe a milling machine. I do not plan on using 100A but I would like the option down the road if necessary.
Unless you plan on running 3 or more of those at the same time, you are way over kill. 60A is more than enough for a 1 man operation.

You would save a bundle by downsizing on wire by downsizing, especially for that length. Remember, you can install a 100A panel and feed it with smaller wire as long as the wire is protected by by a 60A breaker in your main.
 
OP
B

badams14

Member
Joined
Jul 21, 2015
Messages
22
How big should of wire should I use instead of the #6?


Sent from my iPhone using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
The 6 AWG grounding conductor would not be in compliance with 250.122(B). as the ungrounded conductors has been increased from the minimum conductor size required for the installation.

Damnit i always forget about the illogical 250.122(b)...
 