I am not sure how these loads are served, but just to clarify, a GFCI is required for 240 V receptacles, but not direct wired loads.
In Section 210.8(F) of the 2020 NEC, GFCI protection is now required for outdoor “outlets” at dwellings.
An “Outlet”, according to the NEC Article 100 definition, is a point on the wiring system at which current is taken to supply utilization equipment.
Many people make the mistake of thinking that only receptacles can be “outlets”. A receptacle is one kind of outlet, but so is a hard-wired connection such as a ceiling fan, or even a hard wired connection to an outdoor air conditioner.
In the 2020 NEC, all outdoor “outlets” for dwellings, other than lighting, electric snow-melting, deicing, or pipeline heating, that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel. This is a big change that came as a result of a child's death. Here is the link to the reason behind the code change:
https://www.juryverdictreporters.com/.../basi.../page14.html