Sub Panel Inspection

slush

Well-known member
Joined
Sep 6, 2011
Messages
46
I had my sub panel inspection earlier this week. For reference, my sub panel is 200' away from the main panel, I pulled two hots, one neutral and a ground, all in proper conduit, buried to depth. When we walked out to the sub panel, he said I couldn't use the ground from the main panel and I had to remove it, and use the grounding rods I sank as the only ground. Everything I've read points to this as being incorrect, is it? He approved the installation, but I want to make sure it's done properly and with the greatest amount of safety as possible.

O4YHgDu.png

FYI: They are using 2014 NEC


Thanks
 
To avoid these ads, REGISTER NOW!

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
I believe your inspector is wrong unless there is a local amendment to NEC.

See NEC 250.32(B)(1)

"Supplied by a Feeder or Branch Circuit: An equipment grounding conductor, as described in 250.118, shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s)."

Above text from 2017 NEC, but I believe this has been a requirement since early 2000s. There is an exception for previously installed feeders, so if you are replacing a panel at the detached structure you don't need to install a separate grounding conductor from the main panel.
 
OP
S

slush

Well-known member
Joined
Sep 6, 2011
Messages
46
I believe your inspector is wrong unless there is a local amendment to NEC.

See NEC 250.32(B)(1)

"Supplied by a Feeder or Branch Circuit: An equipment grounding conductor, as described in 250.118, shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s)."

Above text from 2017 NEC, but I believe this has been a requirement since early 2000s. There is an exception for previously installed feeders, so if you are replacing a panel at the detached structure you don't need to install a separate grounding conductor from the main panel.
Nope, new service. He even told me that I could pull the entire conductor out of the run (which I'm not going to do).
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
The ground setup the inspector is allowing mimics what we used to do in Canada for buildings with livestock (especially sensitive to ground potential).

I don't see any hazard. There's a number of sound ways to do things and Code usually ends up picking one flavour.
 
To avoid these ads, REGISTER NOW!

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Code has required a separate ground conductor on sub-panels since 2008 IIRC, so using 2014 NEC would also include this requirement.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The ground setup the inspector is allowing mimics what we used to do in Canada for buildings with livestock (especially sensitive to ground potential).

I don't see any hazard. There's a number of sound ways to do things and Code usually ends up picking one flavour.
I guess you missed that the OP said the bonding screw in the sub was removed. Earth ground is not good for clearing fault current.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
One more vote that the inspector does not have a clue. A sub panel has to have a equipment ground pulled from the panel it is fed from.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
I guess you missed that the OP said the bonding screw in the sub was removed. Earth ground is not good for clearing fault current.
Oops ya, missed that... what I was commenting would have the neutral bonded at the sub.
 

andyvh1959

Well-known member
Joined
Feb 15, 2020
Messages
2,590
Location
Green Bay WI
Here in Green Bay I was required to connect a ground from the main panel to the sub panel feeding power to my new detached garage. Also, the detached garage required two ground rods (minimum six feet apart) connected to the ground bus bar. So the diagram the OP included agrees, with the exception of the 2nd ground rod.
 
OP
S

slush

Well-known member
Joined
Sep 6, 2011
Messages
46
Here in Green Bay I was required to connect a ground from the main panel to the sub panel feeding power to my new detached garage. Also, the detached garage required two ground rods (minimum six feet apart) connected to the ground bus bar. So the diagram the OP included agrees, with the exception of the 2nd ground rod.
Sorry, that diagram doesn't show the second grounding rod. I did sink two 8' rods with greater than 6' apart.
 