Sub panel install question.

rbragg

Member
Joined
Jan 6, 2020
Messages
7
Location
Texas
I have been building a house. While building I have run a 100 amp sub panel directly off my meter. Now that the house is almost done I will be wiring it directly into my house panel. My question is.

My panel is on the outside of my house. I have a knockout on the side big enough and almost a strait shot to the breaker I will be using. I was thinking about using a 2 1/2 in conduit body to tie into the side. Then run to my 2 1/2 in conduit.

When I mentioned this to my friend (He used to do electrical in the oil field)he said to go into the bottom. I have two issues with this.

1-no knockouts are big enough

2-bending the wire I have 90 degrees will not be easy.

My friends issue with going in the side is water leaking. So I guess my question is will this be a issue? Or is there a way to make it not a issue?

Thanks
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I have been building a house. While building I have run a 100 amp sub panel directly off my meter. Now that the house is almost done I will be wiring it directly into my house panel. My question is.

My panel is on the outside of my house. I have a knockout on the side big enough and almost a straight shot to the breaker I will be using. I was thinking about using a 2 1/2 in conduit body to tie into the side. Then run to my 2 1/2 in conduit.

When I mentioned this to my friend (He used to do electrical in the oil field)he said to go into the bottom. I have two issues with this.

1-no knockouts are big enough

2-bending the wire I have 90 degrees will not be easy.

My friends issue with going in the side is water leaking. So I guess my question is will this be a issue? Or is there a way to make it not a issue?

Thanks

A panel coming directly off a meter with no disconnect between them is a main service panel and should be wired with a bonded neutral not wired as a subpanel.

Now that you have a main service panel, you need to make sure the subpanel has an isolated neutral. The feeder will need to be 4-wire. you will also probably need some ground bar kits.
 