Sub panel wiring question

dmaxfireman

Well-known member
Joined
May 12, 2019
Messages
190
Location
CT
I am looking to run 'SER' across basement to exit point through foundation, then into junction box and splice to 'MHF' in conduit and run underground to a garage where it will come back up and transition through the wall and directly into the back of the panel. The splice at the house junction box would be made using polaris connectors.

Question, is it legal to splice 2-2-2-4 SER to 2-2-4-6 MHF? Those are the sizes I can find locally without ordering online.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
What are your loads? Number of workers?

Youre probably fine with the reduced neutral...

Have you considered running MHF the entire way? Would need to be in conduit in the buildings but end to end is best.
 
OP
D

dmaxfireman

Well-known member
Joined
May 12, 2019
Messages
190
Location
CT
The SER run will be about 40-50ft with bends, the MHF will be a 100ft run with drop underground and rise into panel. Conduit in the house will be more of a headache than it would be worth I think but not 100% opposed to the challenge.

I was going to put it on a 70amp breaker in the main panel from the online calculator I used.

Loads will be,
15a 120v led lights
15a 120v receptacles
15a 120v receptacles
30a 240v compressor
50a 240v welder
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Are the loads you listed actually circuit sizes? Make the receptacle circuits 20A.
 