Hi Everybody- I have a subpanel that is fed with 2/0 in a barn down the hill from my house.
I take it that this "pole barn" is
NOT the "Wood Shop" building that was under so much discussion in your other thread
http://www.garagejournal.com/forum/showthread.php?t=216567?
The feed is Aluminum. The problem I see is the feed hots are too large for the breaker screws. The previous owner snipped some Aluminum off, capped the hots to #4 tails and inserted the #4 in the breaker in order to get juice.
We need more information.
First, what is the rating of this "Main" circuit breaker you're referring to, and where exactly is it installed? Based on your referring to it as a "Main" breaker, I am inferring that this is the "local disconnect" breaker in the sub-panel itself.
Second, what is the rating of the circuit breaker FEEDING this 2/0 cable at the main panel or meter box?
Third, what is the total run length of this cable, panel to panel?
Does this seem crazy to you?
Well, I certainly would not call it "kosher"; and I definitely don't care for the manner in which he joined the wires. But having said that, the situation MAY not be quite as bad as it would at first appear to be.
The fact that the breaker(s) in question are apparently intended for relatively small (relative to 2/0 anyway) wires implies that they are also rated for relatively low trip currents. From this, it follows that the LIKELY reason someone used a 2/0 feeder is because the run length was long enough that a smaller wire would have induced too much voltage drop.
IF this is the case, the 2/0 wire is presumably not strictly needed from an "ampacity" standpoint; and so, a significantly smaller wire MIGHT actually be adequate for the maximum current the breaker(s) will allow anyway. Still, AWG 4 does strike me as a rather large difference from AWG 2/0 for this to be COMPLETELY plausible, unless that run length is insanely long (also, copper vs. aluminum could explain part of it; but that would raise still more issues with how the wires were joined). In any event, even at AWG 4, it certainly won't be imposing significant voltage drop over a run length of a few inches to a couple feet (but that's the least of the issues).