I need to run another subpanel from my main lug attached to my meter. I already have one panel run from this location. Can I add another panel from this main? I don't see where I could tie the neutral in to this panel.
Than main lug is 200 amp and I need to run a 100 amp sub panel 330' and am considering 2/2/2/4 direct bury. Any input would be greatly appreciated.
BillK - I do plan on installing a 100 Amp breaker and connecting the conductors to that and then run to the sub-panel. I guess at this point, I just need to make sure of wire size so I can hook up to the breaker that I install.
OK, now that SOME of the intervening confusion has been cleared up, a few points...
First, at the distance you need to run, that "2/2/2/4 direct bury" will be grossly inadequate, regardless of whether it is copper or aluminum. To feed 100 Amps 330 feet using aluminum wire will require AT LEAST AWG 4/0 main conductors. To go lighter than this will lead to excessive voltage drop. However, earlier in the thread you also mentioned not usually needing more than perhaps 30-40A at the sub-panel; so
IF you can live with a 60A breaker at the source end, you can get away with AWG 2/0 (which would be MUCH more cost-effective).
Second, and also considering the distances involved, have you consulted with your local power company to determine the costs of adding a second service drop (with its own meter), much closer to where you actually need the power? They will likely charge for this, perhaps including an extra monthly fee if they think you are a "commercial" customer; but it may well be your best bet in the long run, for several reasons: You would save the cost (and installation hassle) of that huge oversized feeder cable, AND you could presumably have as much juice as you want in the outbuilding.