Subpanel question
branimal
I am installing a subpanel on the 2nd floor. The main panel is in the basement. The #3 wires are coming in from the bottom of the subpanel.
The subpanel lugs are on the top of the box.
Should I :
1. Run the #3 wires inside the box, along the perimeter to the top of the subpanel to the lugs.
2. Or simply flip the box upside down and make a short run to the lugs.
larry4406
Northern Virginia
Definitely not. Put the lugs on top.
Why? Canada thing?
Note how the keyhole slots in the back of the panel accommodate hanging with either end being up.
OP has a main lug panel (no breaker) so no breaker handle orientation to worry about.
Nothing wrong with bottom fed main lug panel unless prohibited by the panel manufacturer. In the OP's case, bottom fed will make a neater installation since the wire is coming from the bottom.
branimal
Installed her upside down. Thanks guys.
mike93lx
Richmond, VA
branimal
Norcal
There NO such thing as a upside down panel unless it's a model from decades past that has a vertically mounted main circuit breaker where ON is up, instead of the predominate style used today with a horizontally operated main, they are either top feed or bottom feed & it's effing moronic to terminate the feed from the opposite end it's fed from. There are some exceptions like the classic Cutler-Hammer CH loadcenters from when they first came out in the late 50's until about 25 years ago where the dead front looked dorky when turned where the main lugs were at the bottom.
Chuckster in NJ
Hunterdon County NJ
Can't tell...did you get a bushing on the conduit fitting in the box?
A GROUNDING BUSHING is required if this conduit is installed in a "concentric or eccentric knock out"………. Looking at the location of the 1 1/4” conduit it "MAY" be installed in a "factory" concentric knock out.
mike93lx
Richmond, VA
He has a separate egc. Worrying about a grounding bushing or set screw is not applicable
mm08822
There's a set screw missing on the coupling closest to the panel.
To use the EMT as a grounding conductor the EMT must be properly installed
All set screws are required for proper conduit install otherwise couplings/connectors are not being used as directed by mfr. A separate equipment grounding conductor won't change that requirement.
mm08822
While a good practice, it's only required for service entrance raceways and conduits for circuits greater than 250v to ground.
branimal
Great eyes. I know about the missing set screw. Dropped into a shaftway. I’ll grab a screw off another coupling.
Chuckster in NJ
Hunterdon County NJ
Very true! I could never understand why you need it on over 250 volts and NOT needed on under 250 volts.……… It is always a good practice to take the extra step on bonding and grounding.