I am installing a subpanel on the 2nd floor. The main panel is in the basement. The #3 wires are coming in from the bottom of the subpanel.

The subpanel lugs are on the top of the box.

Should I :
1. Run the #3 wires inside the box, along the perimeter to the top of the subpanel to the lugs.
2. Or simply flip the box upside down and make a short run to the lugs.
 

Attachments

  • IMG_6661.JPG
    IMG_6661.JPG
    775.3 KB · Views: 142
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,562
Location
Northern Virginia
Definitely not. Put the lugs on top.
Why? Canada thing?

Note how the keyhole slots in the back of the panel accommodate hanging with either end being up.

OP has a main lug panel (no breaker) so no breaker handle orientation to worry about.

Nothing wrong with bottom fed main lug panel unless prohibited by the panel manufacturer. In the OP's case, bottom fed will make a neater installation since the wire is coming from the bottom.
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,943
Installed her upside down. Thanks guys.
 

Attachments

  • 80DF17B6-0969-4AFE-815D-E5882D22B9D7.jpeg
    80DF17B6-0969-4AFE-815D-E5882D22B9D7.jpeg
    1.2 MB · Views: 132

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,894
Location
Richmond, VA
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,943

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Installed her upside down. Thanks guys.
There NO such thing as a upside down panel unless it's a model from decades past that has a vertically mounted main circuit breaker where ON is up, instead of the predominate style used today with a horizontally operated main, they are either top feed or bottom feed & it's effing moronic to terminate the feed from the opposite end it's fed from. There are some exceptions like the classic Cutler-Hammer CH loadcenters from when they first came out in the late 50's until about 25 years ago where the dead front looked dorky when turned where the main lugs were at the bottom.
 
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,319
Location
Hunterdon County NJ
Can't tell...did you get a bushing on the conduit fitting in the box?
A GROUNDING BUSHING is required if this conduit is installed in a "concentric or eccentric knock out"………. Looking at the location of the 1 1/4” conduit it "MAY" be installed in a "factory" concentric knock out.
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,894
Location
Richmond, VA
A GROUNDING BUSHING is required if this conduit is installed in a "concentric or eccentric knock out"………. Looking at the location of the 1 1/4” conduit it "MAY" be installed in a "factory" concentric knock out.
He has a separate egc. Worrying about a grounding bushing or set screw is not applicable
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
There's a set screw missing on the coupling closest to the panel.
To use the EMT as a grounding conductor the EMT must be properly installed
All set screws are required for proper conduit install otherwise couplings/connectors are not being used as directed by mfr. A separate equipment grounding conductor won't change that requirement.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
A GROUNDING BUSHING is required if this conduit is installed in a "concentric or eccentric knock out"………. Looking at the location of the 1 1/4” conduit it "MAY" be installed in a "factory" concentric knock out.
While a good practice, it's only required for service entrance raceways and conduits for circuits greater than 250v to ground.
 
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,943
There's a set screw missing on the coupling closest to the panel.
To use the EMT as a grounding conductor the EMT must be properly installed
Great eyes. I know about the missing set screw. Dropped into a shaftway. I’ll grab a screw off another coupling.
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,319
Location
Hunterdon County NJ
While a good practice, it's only required for service entrance raceways and conduits for circuits greater than 250v to ground.
Very true! I could never understand why you need it on over 250 volts and NOT needed on under 250 volts.……… It is always a good practice to take the extra step on bonding and grounding.
 