Subpanel

23 CHIEF

Well-known member
Joined
Jul 24, 2013
Messages
150
Location
Buffalo NY
85364ad2cde38c803e1dcfb54d5b57fc.jpg


Does this panel look like it's set up right for a detached garage subpanel I am gonna us the bar that's bonded to the panel for ground
 
To avoid these ads, REGISTER NOW!

Redwolf947

Well-known member
Joined
Feb 13, 2015
Messages
613
Location
South East WI
I'd move that Lug to the other buss bar. Your ground wire will be smaller than your neutral.. I'd rather have more room for neutrals than grounds you can put more than one ground wire under a screw (the instructions say how many and what size). But you can't put more than one neutral in (double tap). Otherwise Yes looks OK to me. others will chime in I'm sure.

I'm Curious sberry why use the smaller bar for neutrals?

Disclaimer I'm not an electrician.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Did the panel come with a lug in a bag,the screws are missing on that bar where the lug should be,so either it was taken out or it's separate
 
OP
2

23 CHIEF

Well-known member
Joined
Jul 24, 2013
Messages
150
Location
Buffalo NY
I think I will move the lug or not even use it I'm using 6-3 uf and the conductors fit right in the bar
 
To avoid these ads, REGISTER NOW!

bromz

New member
Joined
Apr 21, 2014
Messages
1
Remove the bond strap. You should only bond at the first panel. Then keep your grounds and neutrals separate in the sub panel.


Chris
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I'd move that Lug to the other buss bar. Your ground wire will be smaller than your neutral.. I'd rather have more room for neutrals than grounds you can put more than one ground wire under a screw (the instructions say how many and what size). But you can't put more than one neutral in (double tap). Otherwise Yes looks OK to me. others will chime in I'm sure.

I'm Curious sberry why use the smaller bar for neutrals?

Disclaimer I'm not an electrician.

^^^ THIS^^^

Remove the bond strap. You should only bond at the first panel. Then keep your grounds and neutrals separate in the sub panel.


Chris

In this case, no, because BOTH bars are insulated from the panelboard housing. The ground needs to be bonded to the housing.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Got your info needed above from Charles (in GA) . . .
. . . . . . fixed your subpanel PIC so orientation easier to view.
 

Attachments

  • 23 Chief_subpanel_GJ.jpg
    23 Chief_subpanel_GJ.jpg
    143.8 KB · Views: 65
Last edited: