I'm installing a Goodman 3.5 ton heat pump. I have a question about the suction line. Because my air handler is more than 25' away Goodman is recommending going from 7/8" to 1 1/8" on the suction line.

The unit looks to be setup with a female swagged fitting for 7/8" but I noticed the 1 1/8" line fits over the outside of the fitting with a degree of sloppiness. I'm wondering if the intent is to silver solder the 1 1/8" line directly over these fittings or should I purchase a reducer for both the condenser and evaporator.
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Not finding ARC rated reducer. Might you know a supplier? Regrlare water pipe reducer OK?

Mueller W 01049, they use that same part# for both a 7/8"x1 1/8" refrigeration fitting and a 3/4"x 1" sweat water fitting.

Water line fitting will likely be just fine as long as you avoid the cheapest china made stuff.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
What is the difference between:

Muller W 01049 1 x 3/4 Inch Copper Pipe Reducer Coupling – C x C, Solder Joint.

Muller W 01337 1 x 3/4 Inch Copper Pipe Reducer – Ftg x C, Solder Joint
 
To avoid these ads, REGISTER NOW!

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,187
Location
Arkansas
Whats the SEER rating of the unit? i see no reason at all on up to a 50 ft run with no more than 10ft of rise to upsize at all.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
What is the difference between:

Muller W 01049 1 x 3/4 Inch Copper Pipe Reducer Coupling – C x C, Solder Joint.

Muller W 01337 1 x 3/4 Inch Copper Pipe Reducer – Ftg x C, Solder Joint

The second one looks to be a fitting reducer, the 1" side would be sized to go inside a fitting rather then over the pipe, in other words the 1" side would be the same diameter as the pipe.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Whats the SEER rating of the unit? i see no reason at all on up to a 50 ft run with no more than 10ft of rise to upsize at all.

Seer is 16. The 1 1/8 is as recommended by the manufacture from 26 to 50 ft. At this point I already have the lineset.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
The second one looks to be a fitting reducer, the 1" side would be sized to go inside a fitting rather then over the pipe, in other words the 1" side would be the same diameter as the pipe.

Cheep enough I will order both. Thanks
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,187
Location
Arkansas
Also to answer the ftting quetion, no, regular plumbing fittings are no good here. Any HVAC supply house will have the right ones.
 