low flow fixtures also add significantly to hot water delivery time on any system, unless you have a hot water circulating system.
Bathtubs can be a problem with tankless, depending upon the water fill line size of the tub faucet and the tub size. If you have a 3/4" supply or one of those "waterfall" type spouts you will not get the same "visual affect" with a tankless as a tank, but the tankless will fill the tub. The 3/4" fill can supply up to 10-12 gpm. The tankless will regulate the flow to guarantee temperature is at the set point on the unit. That is usually 120*.
I will use Rinnai as an example as I've worked with them since '91, use them in my homes and am a technical trainer for them. I will not use the 199,000btu units as that is much larger than what the OP requires. The RUC-80i is a .95 EF unit with a max input of 152,000 btu. When in the winter your supply temps drop, and that is dependent upon where your water originates, the units output will decline. (In my MA home I usually saw a 5-10* drop for about 3 month of the year. With my current well the temps are consistent year round.) Specifically, the RUC80i at at 50, 60 or 70* temp rise will produce 5.9, 5.0, & 4.2 gpm respectively...all day long. If you sit in a bathtub over 105* you are no longer bathing but par-boiling, so that is the max temp.
Tankless water heaters, at least the good ones, are designed to guarantee temp at the expense of pressure. In this case if you tried to fill a tub with that 3/4" supply the unit would reduce the flow to guarantee temperature and with that RUC80i you would likely fill the tub at around 5 gpm. I have a 40 gal clawfoot tub and it takes about 5-8 minutes to fill the tub. I'm not suffering.
The number one mistake in tankless installations is inadequate gas line sizing. You may not need to increase the size of the gas line IF THE EXISTING SYSTEM CAN SUPPORT IT, but eyes open on this. You can pipe them with 1/2" pipe but the system has to be spot on to make them work. 3/4 gives more margin for error.
Location matters. Don't put it out in the N 40. Try to stay close to the primary point of use. The RUC80 can vent with PVC pipe or with the proprietary concentric poly-propylene 5" pipe. If you are on an outside wall, use the concentric pipe. If in the middle of the house the pvc may be a better option. The concentric is one 5" hole in the wall. The PVC has two 3".
In the past recirc systems for tankless have been a problem. Today, you can use Rinnai's new wireless module to operator the recirc system. Install a wireless push button up under the kitchen cabinet and the wireless motion sensor in the M Bath. You can control the water heater on your mobile device and also receive error codes if the unit is not happy. It is a slick system and is backwards compatible to all Luxury and Ultra series Rinnai's made since '06. V series does not have the Circ-logic so no go there.
For a couple days, pay attention to exactly how many minutes a day you actually have a hot tap open. I think you will be surprised at how seldom out of 24 hrs you are drawing hot water. I put in my first unit in our home when my girls were middle school. My gas bill dropped by 40%. It should have been greater savings, but once people know that they are not going to run out of hot water they tend to linger a bit more. Better comfort in other words. No one ever ran out of hot water. Years later a classmate friend of my daughters was getting married. We had a house full of kids. About 18-20 people showered and we never ran out of hot water. Now in our new home it is just the two of us but hot water is never an issue.
Hire a good guy who has attended the factory training. Get off on the right foot.
I have a really good plumber I use. My entire house is Propane. I did an analysis and thankless water heaters do not save. My gas company that I have used for 18 years the techs also told me the same thing. Unless like other her said if you have a 2nd house than it is great. I installed a efficient 50 gallon gas heater it cost a few dollars a month and I have 3 kids. Most of the hype of things like Tankless are just that. Like High efficient as systems... Hype.
Sure would be nice if you would publish the true installed cost of these tankless units.
It like saying l love my new commuter car and I save $50 per month on gasoline. Oh by the way I spent $50k on my electric car. One other issue .....I can’t take my new car on vacation 500 miles without stopping 3 times to charge it up. I almost forgot .....The home charger cost $3k to install and my insurance doubled.
I bought a 24kw tankless electric water heater from home depot for $324. I spent $30 on three breakers, $40 on 6 gauge wire, and $20 on conduit. I was able to re use the PEX tubing from my old tank water heater. I installed it myself. Total ~$415.
If you dont want to DIY the install, then expect to pay an electrician at least $300-500 (or more if your WH is far away from your breaker panel, 6 guage wire is $$$). If your main panel is out of space for the additional breakers or less than 120AMPs then add another 1-3k for install cost for an upgrade to your panel.
I agree its expensive if you pay to have it installed then the costs can anywhere from expensive to astronomical. DIY is very easy if you have the space in your panel and its close to your panel.
I have nat gas in my house, and went with an electric unit because I only pay .12c per KWH. Natural gas tankless water heaters also cost significantly more than electric ones.
So heating 50 gallons of water 24/7/365 vs. only heating what you use doesn't save? Come on man, that doesn't even pass the common sense test. ?
It can make common sense.......
Tank unit might be 30-50k btu.
Tankless unit might be 199,000 btu
When the tankless is running it can consumes 4-5 times the gas. Tankless really save money if you don’t use them. Have a large family and endless supply of hot water from the tankless ............your water bill, sewer bill and gas bill might actually go up.........when those teenagers figure out they can take 20-30 minute showers.
So depending on use the two units might have similar operating costs.
Look at the energy guide yellow labels:
Tankless might be $204-230per year and tank might be $240-280
https://images.homedepot-static.com/catalog/pdfImages/cd/cd5ee660-b8b8-4222-b7ff-c6a36ee95e77.pdf
https://images.homedepot-static.com/catalog/pdfImages/c1/c15ab1d3-59dd-4c3a-b6f6-5a74964b4b85.pdf
it takes the same amount of energy (BTU) to heat the same amount of water to the same temp. rate of consumption does not indicate total energy used.
rate of consumption over time does.

I know the costs but others reading and posting do not.
I am all about DIY........but many on the forum disagree and want permits especially on new circuits and NAT gas piping. Then there’s the warranty issues on expensive heaters when installed DIY. Then there’s the lack of parts in the DIY market place for some brands.
We have talked about NAT gas costs. My water heating bill with NAT gas is about $10 per month on tank model. I would never ever consider an electric water heater. I do not find .12 per kw cheap or cost effective way to heat water. Especially when NAT gas is in the building.
It can make common sense.......
Tank unit might be 30-50k btu.
Tankless unit might be 199,000 btu
When the tankless is running it can consumes 4-5 times the gas.
While not "wrong" this statement is misleading. A 199,000 btu tankless will modulate its fire depending upon flow rate and delta T, from as low as 15000 btu UP TO 199,000 btu. In other words it will fire anywhere in 1000 btu increments. The actual formula to determine the firing rate is GPM X Delta T X 500 = BTU. Unless I am running the bath-tub my tankless unit NEVER sees max input. On my tankless I can read the GPM to within .1 gpm on the digital display. As an example, my shower here in CA is a 2.5 gpm flow rate. I use 1.9 gal of hot mixed with .6 gal of cold with my unit set to produce 120* water. So 1.9x55x500=52,250 btu for my shower. Back east in MA the same flow rate shower head took 2.1 gal of hot and the water supply was colder, so 2.1x65x500=68,250 btu input. As my gas supply is sized correctly I can, with my 180,000 btu tankless run both showers and another fixture all day long if I choose to do so.
We have 2tankless water heaters in our vacation home. When we aren’t there all we are charged is the basic $10 mo. facilities charge. The previous unit was $28 mo. In our permanent residence our gas charge was $18.87 last mo. All 3units are rinnais. I would never go back to an old school water heater.
It can make common sense.......
Tank unit might be 30-50k btu.
Tankless unit might be 199,000 btu
When the tankless is running it can consumes 4-5 times the gas.
While not "wrong" this statement is misleading. A 199,000 btu tankless will modulate its fire depending upon flow rate and delta T, from as low as 15000 btu UP TO 199,000 btu. In other words it will fire anywhere in 1000 btu increments. The actual formula to determine the firing rate is GPM X Delta T X 500 = BTU. Unless I am running the bath-tub my tankless unit NEVER sees max input. On my tankless I can read the GPM to within .1 gpm on the digital display. As an example, my shower here in CA is a 2.5 gpm flow rate. I use 1.9 gal of hot mixed with .6 gal of cold with my unit set to produce 120* water. So 1.9x55x500=52,250 btu for my shower. Back east in MA the same flow rate shower head took 2.1 gal of hot and the water supply was colder, so 2.1x65x500=68,250 btu input. As my gas supply is sized correctly I can, with my 180,000 btu tankless run both showers and another fixture all day long if I choose to do so.
The rest of the story is.........
Then there is the cold climate where the inlet water temp is 34-42* winter and summer 42-48* summer.
On the other post about stand by losses ........just received my Sept NAT gas bill. 45.2 therms $9.43 for hot water, gas dryer gas cook top. In the grand scheme standby is not a concern as it might be $2.00 per month ?
So my gas fired tank water heater sprung a leak and I am debating whether or not I should switch to a tankless water heater.
From what I read online, the biggest complaint is that they don't heat the water enough and don't get past 120. We have a large jacuzzi tub that needs a lot of water and don't want it to be lukewarm.
Any issues with the temp from these?
So my gas fired tank water heater sprung a leak and I am debating whether or not I should switch to a tankless water heater.
From what I read online, the biggest complaint is that they don't heat the water enough and don't get past 120. We have a large jacuzzi tub that needs a lot of water and don't want it to be lukewarm.
Any issues with the temp from these?
I have a really good plumber I use. My entire house is Propane. I did an analysis and thankless water heaters do not save. My gas company that I have used for 18 years the techs also told me the same thing. Unless like other her said if you have a 2nd house than it is great. I installed a efficient 50 gallon gas heater it cost a few dollars a month and I have 3 kids. Most of the hype of things like Tankless are just that. Like High efficient as systems... Hype.
^Matt Risinger is the biggest paid advertisement toolbag out there.
I'd trust a 10 year old before anything that he pitches on youtube.
When the conventional HWH reaches this state, if there were some way to monitor it for lets say 30 days to see how much power it consumes just maintaining tank temp without any usage, I think then it would be a good example of comparing apples to apples.
When we moved out of the old house I forgot to turn the water heater off. After I noticed it was still on and cut it off the light bill went down over $10 a month. That's at 10 cents per kwh so over 100kwh per month in standby losses.
I'd already decided on a tankless for the new place, mostly because there isn't a good place for a tank, before I found out how much the old tank was costing.
^Matt Risinger is the biggest paid advertisement toolbag out there.
I'd trust a 10 year old before anything that he pitches on youtube.
From what I have looked into, I would say for the most part, that his video was right on.
I have a 16-year-old, 75 gallon, Bradford White water heater. It looks like the current price to replace it is around $1,200. I can get a top of the line, 200k Rheem or Rinnaui tankless for around $1,500. (I already have a dedicated recirc line with a pump). At this point, I am probably going to go tankless when it starts to show signs of failure.
Why - mainly because the replacement 75 gallon heater weighs around 260 lbs and I have to get it 18" up and over to it's stand and number two is I will regain some space in my garage. Lastly, a good tankless should last 20 years
How old was the heater?
Is the present HWH electric?
From what I have looked into, I would say for the most part, that his video was right on.
I have a 16-year-old, 75 gallon, Bradford White water heater. It looks like the current price to replace it is around $1,200. I can get a top of the line, 200k Rheem or Rinnaui tankless for around $1,500. (I already have a dedicated recirc line with a pump). At this point, I am probably going to go tankless when it starts to show signs of failure.
Why - mainly because the replacement 75 gallon heater weighs around 260 lbs and I have to get it 18" up and over to it's stand and number two is I will regain some space in my garage. Lastly, a good tankless should last 20 years