Well-known member
I have a sub panel in my garage coming from the main in the basement with 8-3 Non-Metallic sheathed cable from a 40 amp double pole breaker.
But, out in the garage, the hot tub is wired in the box with a 50 amp breaker. Is this alright? Doesn't seem like you should have a higher amp breaker than the one it is connected to in the house. If not, what should or could be done? Can I replace the 40 amp in the basement to a 50 amp with the 8-3 wire? Can this be done? Any other suggestions?
But, out in the garage, the hot tub is wired in the box with a 50 amp breaker. Is this alright? Doesn't seem like you should have a higher amp breaker than the one it is connected to in the house. If not, what should or could be done? Can I replace the 40 amp in the basement to a 50 amp with the 8-3 wire? Can this be done? Any other suggestions?