This don't seem right to me...

scott_one

Well-known member
Joined
May 3, 2010
Messages
106
Location
Lapeer, MI
I have a sub panel in my garage coming from the main in the basement with 8-3 Non-Metallic sheathed cable from a 40 amp double pole breaker.

But, out in the garage, the hot tub is wired in the box with a 50 amp breaker. Is this alright? Doesn't seem like you should have a higher amp breaker than the one it is connected to in the house. If not, what should or could be done? Can I replace the 40 amp in the basement to a 50 amp with the 8-3 wire? Can this be done? Any other suggestions?
 

Attachments

  • DSCF5602.jpg
    DSCF5602.jpg
    144.2 KB · Views: 114
  • DSCF5609.jpg
    DSCF5609.jpg
    134.7 KB · Views: 114
  • DSCF5607.jpg
    DSCF5607.jpg
    139.3 KB · Views: 103
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you have bigger problems than that. the breaker in the middle pic looks discolored like its overheating from being overloaded. The subpanel has grounds landed on the neutral bar, i cant tell if its bonded to the can or not. You need to get an electrician over there to clean this up. you cannot put the 8/3 on a larger breaker. What else does the subpanel supply?
 

Grumpy365

Well-known member
Joined
Jan 21, 2010
Messages
623
Location
Brazoria County Texas
So it trips on the house panel before it trips on the sub panel, as long as it trips your good to go.

My hot tob panel is all GFI Breakers. While i am generally not a huge fan of GFI on a hot tub i wouldn't be without one .
 
OP
S

scott_one

Well-known member
Joined
May 3, 2010
Messages
106
Location
Lapeer, MI
you have bigger problems than that. the breaker in the middle pic looks discolored like its overheating from being overloaded. The subpanel has grounds landed on the neutral bar, i cant tell if its bonded to the can or not. You need to get an electrician over there to clean this up. you cannot put the 8/3 on a larger breaker. What else does the subpanel supply?

It supplies the lights and electrical outlets, the garage door opener and an outlet for a stove on a 30 amp double pole breaker (and also the hot tub).
By bonded to the can, do you mean attached? It sits in the plastic, I can't see that it is attached to the box at all.
 
To avoid these ads, REGISTER NOW!
OP
S

scott_one

Well-known member
Joined
May 3, 2010
Messages
106
Location
Lapeer, MI
So it trips on the house panel before it trips on the sub panel, as long as it trips your good to go.

My hot tob panel is all GFI Breakers. While i am generally not a huge fan of GFI on a hot tub i wouldn't be without one .

Grumpy, are these the GFI Breakers? They are in a subpanel out back by the hottub.
 

Attachments

  • DSCF5612.jpg
    DSCF5612.jpg
    159.9 KB · Views: 45

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
that subpanel is overloaded. get an electrician over there to fix everything
 