Trying to set up interlock switch. Large distance between main and generator breaker.

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
Hello,

I am having a hard enough time trying to envision setting this thing up since most videos and instructions are geared for the main to be at the top only to take a measurement and notice that the distance between the main and the breaker intended to be used for the generator is about 4 inches away.

All of the products that I see on Amazon seem to be geared to 2 inches or less.

Any suggestions?

Thanks.

lCPSJOm.jpg

vVH3kuu.jpg

z8HZhgj.jpg




lECVjdF.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
Looks just like my homeline panel that I added an interlock kit to. Buy the square d one, not a generic POS
Sure does. What is the distance between the main and the 2 breakers at the left? Would you mind slinging me a link to the one that you bought please? Thank you.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
Sure does. What is the distance between the main and the 2 breakers at the left? Would you mind slinging me a link to the one that you bought please? Thank you.
I may have to walk back my generic POS comment...well at least the generic part. Quality of the kit i bought us fine

Generator Interlock Kit Compatible with Square D Electric HOMCGK2C Homeline Cover Generator and QOM2 Frame Size Main Breaker Interlock Kit https://www.amazon.com/dp/B08ZMYKVFF/?tag=atomicindus08-20

The grey strip between the main and the generator breaker is 1-3/8". Looks the same as yours
 
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684

that measurement they show seem right for yours?
Sorry missed this post. I see how you are measuring this. Is the way that you showed the standard way of measuring things e.g. at the panel? Thank you.
 
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
I may have to walk back my generic POS comment...well at least the generic part. Quality of the kit i bought us fine

Generator Interlock Kit Compatible with Square D Electric HOMCGK2C Homeline Cover Generator and QOM2 Frame Size Main Breaker Interlock Kit https://www.amazon.com/dp/B08ZMYKVFF/?tag=atomicindus08-20

The grey strip between the main and the generator breaker is 1-3/8". Looks the same as yours

Thank you. So it looks to be all about the grey stip. I was thinking just my luck...another science project is all that I need in my life. :)
 
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
Whats with the lock shackle on that breaker?
I have been wondering that forever and I finally got around to googling the right term....


Yep, mine is 1 3/8 like yours....just ordered the POS lol. I hope it "I" hope it's not too much a pain to install. At least I have your pictures. Appreciated.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
Oh, I get the purpose, just curious why you have it. Looks like you don't know either :) probably was just in stock at the time. I see another in your panel too
 
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
Oh, I get the purpose, just curious why you have it. Looks like you don't know either :) probably was just in stock at the time. I see another in your panel too
Well it's somewhat of a distance between the device(s) and the A/C OSU and Water Heater.....several hundred feet. Maybe the last person installed it in an abundance of caution...maybe it is standard practice during installations over here....maybe like you said...it was just in stock.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
Well it's somewhat of a distance between the device(s) and the A/C OSU and Water Heater.....several hundred feet. Maybe the last person installed it in an abundance of caution...maybe it is standard practice during installations over here....maybe like you said...it was just in stock.
They should both have disconnects at the equipment.. If they don't, I'd get some installed
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
looks like you bought the wrong interlock.... is the one you have listed and labeled for your panel? probably not
Who are you referring to? Guessing me?

I did buy a knock off, but it first perfectly fine and is simply a few pieces of bent metal. Functions as designed and is not the "wrong one"

The square d version is 3x the cost. I chose not to go that route but would advocate that anyone else does go that route.
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
There are definitely better interlock kits out there. https://interlockkit.com Makes some nice stuff. They can even do "custom". I've got solar and needed to lock out two double pole breakers (main and solar).
Better than what? The one I have functions perfectly fine. You can't turn the generator on when the main is on and the hold down fits properly. Not sure what better would be
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,883
Location
Austin, TX
Better than what? The one I have functions perfectly fine. You can't turn the generator on when the main is on and the hold down fits properly. Not sure what better would be
Fit and finish thing perhaps. Stainless hardware. The kits above come with drill bits, templates, threadlock - pretty darn hard to screw up. I'm not one to argue that you can't get the same legal function at a fraction of the cost.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
Fit and finish thing perhaps. Stainless hardware. The kits above come with drill bits, templates, threadlock - pretty darn hard to screw up. I'm not one to argue that you can't get the same legal function at a fraction of the cost.
I hope I don't need stainless hardware. Theres plenty in the box that would corrode faster than a zinc played screw. :)

In this case, the edges aren't sharp and the template was sufficient for drilling three holes with my own cheap drill bits

Like I said, I'd encourage anyone to go genuine. Do as I say, not as I do, and all that
 
OP
U

ukiltmybrutha

Well-known member
Joined
Apr 23, 2016
Messages
684
I hope I don't need stainless hardware. Theres plenty in the box that would corrode faster than a zinc played screw. :)

In this case, the edges aren't sharp and the template was sufficient for drilling three holes with my own cheap drill bits

Like I said, I'd encourage anyone to go genuine. Do as I say, not as I do, and all that
I have no problem going generic. I saw that it fits so I am going to run with it!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Who are you referring to? Guessing me?

I did buy a knock off, but it first perfectly fine and is simply a few pieces of bent metal. Functions as designed and is not the "wrong one"

The square d version is 3x the cost. I chose not to go that route but would advocate that anyone else does go that route.
nevermind. i was referring to the OP but looked at the wrong picture.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,032
Location
Coronado, CA
If the correct parts are on hand and you can’t make the unit work, either the parts are not right or the technician is doing something incorrectly.
 
  • Like
Reactions: RPH

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
Looks just like my homeline panel that I added an interlock kit to. Buy the square d one, not a generic POS
It looks a little crooked to me. I suggest a panel change, at least a new cover.

I've installed both Square D and generic interlocks on Square D panels, the same goes for Siemens. They work equally well and are both easy to install. Not sure if there was a listing on the generic interlocks, but if the OE manufacturers can't supply them or the supply houses can't get them, a guy has to do something to git 'r done.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
It looks a little crooked to me. I suggest a panel change, at least a new cover.

I've installed both Square D and generic interlocks on Square D panels, the same goes for Siemens. They work equally well and are both easy to install. Not sure if there was a listing on the generic interlocks, but if the OE manufacturers can't supply them or the supply houses can't get them, a guy has to do something to git 'r done.
Yeah, I probably messed up on one of the holes, C'est la vie, but I have a full demolition of the house scheduled and will make it right in the new build
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,291
Location
Illinois near St. Louis, Missouri
I just got done putting an OEM one on my Homeline panel. Got it off ebay for almost exactly the amazon price. It looks just like the one Mike posted so I found the package label to see if it was OEM or a knock off. It is OEM. That said I wouldn't be worried about a knock off if it fit well. It's just a sliding piece of metal. It's not like it carries any current.
 

60sMotorHead

New member
Joined
Jan 7, 2022
Messages
3
Old thread but always relevant. My friend would need an interlock for a vertical throw main.. more complicated as it's far from where the generator breaker would be. I hope to move the top right doubles down two spaces and put the generator breaker at top right. Friend is waiting for another quote to install a 400a manual transfer switch, which I think is a waste for a 10kva generator. Interlockkit can make one for about $400... which would definitely be less than $11,000 quoted by one guy to install a $1500 Ronk 7416 transfer switch.
 

Attachments

  • 1704684935129.jpg
    1704684935129.jpg
    104.9 KB · Views: 20

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
Old thread but always relevant. My friend would need an interlock for a vertical throw main.. more complicated as it's far from where the generator breaker would be. I hope to move the top right doubles down two spaces and put the generator breaker at top right. Friend is waiting for another quote to install a 400a manual transfer switch, which I think is a waste for a 10kva generator. Interlockkit can make one for about $400... which would definitely be less than $11,000 quoted by one guy to install a $1500 Ronk 7416 transfer switch.
Interlock kit will custom make them? Had no idea... Edit... Until I reread this thread and realized that was previously mentioned
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,857
Location
Richmond, VA
I doubt it would go thru NRTL testing to be listed for that panel.
From their site:

We are proud to have proven products! Wyle Labs – now Element is the original testing lab, granting Interlock Kit certification to retrofit to UL 67 Panelboards. Today, the Interlock Kit line is tested by Eurofins – MET Laboratories, twice annually, for UL compliance.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
From their site:

We are proud to have proven products! Wyle Labs – now Element is the original testing lab, granting Interlock Kit certification to retrofit to UL 67 Panelboards. Today, the Interlock Kit line is tested by Eurofins – MET Laboratories, twice annually, for UL compliance.
Right. Thats for product lines stocked on the shelf or custom made interlocks only made at customers request?
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,909
They should both have disconnects at the equipment.. If they don't, I'd get some installed
Water heaters are allowed to have a permanently installed loto hasp in residential applications, so are dishwashers.
 