Does the equivalent of UF-B (direct burial) exist in 18AWG ? Must have 600V rating.
Nope read aboveDoes the equivalent of UF-B (direct burial) exist in 18AWG ? Must have 600V rating.
Never heard of Tray Cable with 600V and a direct burial rating !![]()
Belden A02182R, 18/2C Type TC Cable, Unshielded, Direct Burial, 600V
New stock due in February 25, 2021www.wireandcableyourway.com
DB and sunlight resistant tray cable seems to go hand in hand, as does 600V. 18AWG tray cable is a little odd, but not unheard of.Never heard of Tray Cable with 600V and a direct burial rating !
Aside from TFFN, you've got TEW and MTW, and I'm sure others, but while all of these may likely be rated for wet locations, they all require conduit, so I'm not sure what you're getting at. OP is looking for DB, so I think TC is the ticket.Smaller then 14 AWG conductors are not building wiring THHN THWN is not made smaller than 14 AWG, 16 gauge is TFFN fixture wire.
Strictly conjecture: if you're looking for 600v rating you will have to go to a #14. Here in Canada I would order 2c #14 TECK90.Does the equivalent of UF-B (direct burial) exist in 18AWG ? Must have 600V rating.
Voltage rating has nothing to do with conductor size, unless it is some obscure code requirement. Voltage rating is related to the insulationStrictly conjecture: if you're looking for 600v rating you will have to go to a #14. Here in Canada I would order 2c #14 TECK90.
Yes indeed. However what I failed to articulate is that where I am I don't think I would find a 600v rated cable in a size less than #14.Voltage rating has nothing to do with conductor size, unless it is some obscure code requirement. Voltage rating is related to the insulation
This is only partially correct. While class 2 is limited to carry 60V, there are plenty of situations where you might need to run class 2 wiring through a class 1 wiring space. In those situations, it is the insulation class that matters, not to keep the 48V (or less in), but to keep the 600V out. An example (not a good one, but a valid one), is 600V rated Cat 6 wire that due to it's rating is allowed to share a conduit with 240V wiring). This product for example is 23 AWG class 2 rated for 600V:I am not the guy who memorized the code book but I recall class 1 wiring had to be 14 gage or larger wires. Class 2 can be small gage wires but are limited to less than 24 volts and 100VA.
So I do not think you can be code compliant need for 18 gage 600v direct burial wire...
Voltage rating has nothing to do wire wire should be.
Read #5 !Yes indeed. However what I failed to articulate is that where I am I don't think I would find a 600v rated cable in a size less than #14.