Unit Heater Sizing Help
buckshot1822
I've read through a lot of prior threads on this subject and they tend to lean towards the smaller end of the btu range vs the calculations that I have seen online.
The general calculations are an estimate for sure, but they come out to me needing around 100k btu. Which is fine if that's actually what I need.
I have a detached 30x50 pole buing with 12' ceilings. It is wrapped in 1/2" foam fanfold and will have r19 fiberglass in the walls and ceiling.
Most likely I will keep the building 45 degrees or so unless I am out there, which case I'd probably try and get it to 60 or 65.
I am in the north central part of PA which zone 6 dips down in to.
Anyone with a similar sized building that can speak to the difference with a say 80k btu unit and a 100k or 125k btu unit. I definitely don't want to oversize and cause it to short cycle etc.
Thanks
buckshot1822
r-19 is very lite for the ceiling . 100 K seems in the ballpark , I nicely do 400 sqft with a 27K with a lot more insulation in the ceiling
It would be light for sure and I may end up going with r30 or r38 on the ceiling. Walls and ceiling will also be covered in 7/16 osb
PoorUB
Fargo, ND
With reasonable insulation you could heat it with a 50,000 BTU heater. I would not go over 75,000 BTU Reznor or Modine.
gmcgeo
Thanks
You need an output of 49,248 BTU. anything over that would be oversized.
yeldogt
Insulation is the cheapest thing you can do .... pays for a lifetime.
With NG and the correct size heater ... proper air sealing you will find keeping the space warmer will be easy and not expensive