Unit Heater Sizing Help

buckshot1822

Member
Joined
Feb 25, 2015
Messages
7
I've read through a lot of prior threads on this subject and they tend to lean towards the smaller end of the btu range vs the calculations that I have seen online.

The general calculations are an estimate for sure, but they come out to me needing around 100k btu. Which is fine if that's actually what I need.

I have a detached 30x50 pole buing with 12' ceilings. It is wrapped in 1/2" foam fanfold and will have r19 fiberglass in the walls and ceiling.

Most likely I will keep the building 45 degrees or so unless I am out there, which case I'd probably try and get it to 60 or 65.

I am in the north central part of PA which zone 6 dips down in to.

Anyone with a similar sized building that can speak to the difference with a say 80k btu unit and a 100k or 125k btu unit. I definitely don't want to oversize and cause it to short cycle etc.

Thanks
 
To avoid these ads, REGISTER NOW!
OP
B

buckshot1822

Member
Joined
Feb 25, 2015
Messages
7
r-19 is very lite for the ceiling . 100 K seems in the ballpark , I nicely do 400 sqft with a 27K with a lot more insulation in the ceiling

It would be light for sure and I may end up going with r30 or r38 on the ceiling. Walls and ceiling will also be covered in 7/16 osb
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,864
Location
Fargo, ND
With reasonable insulation you could heat it with a 50,000 BTU heater. I would not go over 75,000 BTU Reznor or Modine.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
I've read through a lot of prior threads on this subject and they tend to lean towards the smaller end of the btu range vs the calculations that I have seen online.

The general calculations are an estimate for sure, but they come out to me needing around 100k btu. Which is fine if that's actually what I need.

I have a detached 30x50 pole buing with 12' ceilings. It is wrapped in 1/2" foam fanfold and will have r19 fiberglass in the walls and ceiling.

Most likely I will keep the building 45 degrees or so unless I am out there, which case I'd probably try and get it to 60 or 65.

I am in the north central part of PA which zone 6 dips down in to.

Anyone with a similar sized building that can speak to the difference with a say 80k btu unit and a 100k or 125k btu unit. I definitely don't want to oversize and cause it to short cycle etc.

Thanks
You need an output of 49,248 BTU. anything over that would be oversized.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Insulation is the cheapest thing you can do .... pays for a lifetime.

With NG and the correct size heater ... proper air sealing you will find keeping the space warmer will be easy and not expensive
 