Unused neutral lug

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
There is an unused lug similar to this in my GE panel under the row of breakers

Can I use it to ground one of the circuit?

This is main panel with neutral and ground tied

2DM13_AS01
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I do it. If its good for a neutral which is a current carrying conductor which undergoes thermal it will likely be great on a wire that doesn't see use only rarely under a fault, to top that off most of these faults are rather limited, on current limited circuits.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Under the breaker? Make sure that it is not one of two that would be hot pass-through lugs.

A picture of the panel would help.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Under the breaker? Make sure that it is not one of two that would be hot pass-through lugs.

A picture of the panel would help.

It's under the rows and attached to the case, I am sure it is grounded but I will ohm it out.

I would like to add a ground bar at some point but I lost the sticker to the panel so I do not know which bar works for the panel.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
It's under the rows and attached to the case, I am sure it is grounded but I will ohm it out.

I would like to add a ground bar at some point but I lost the sticker to the panel so I do not know which bar works for the panel.

Buy a ground bar kit of the same make as the panel & it will fit.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
Buy a ground bar kit of the same make as the panel & it will fit.

Right now there is 2 white circle stickers that seems to be for a ground bar.. I assume that's where it screws in? Is there any bonding needed for the ground bar, I understand it's a ground bar and for grounding only, not neutrals
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
It's under the rows and attached to the case, I am sure it is grounded but I will ohm it out.

I would like to add a ground bar at some point but I lost the sticker to the panel so I do not know which bar works for the panel.

+1 for pics. if it's not on a bus, just on the panel, i would be hesitant to pass current through it. it may ohm out low but still not be intended to handle current. pics needed.
 