VFD Question

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
I am shopping for a VFD for a 3 phase, 3HP motor. Its for a jointer.

Most VFDs I see for 3HP say 10A. Does that mean the VFD needs 10A, or the motor will be limited to 10A?

My input is 240/20A circuit.

Any input is appreciated?
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,513
Location
Minneapolis
Put up a link to the VFD you're looking at - typically they are rated by their output current, but it will be easier to give a good answer if we can see the specifications.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,313
Location
NJ
Typical specs refer to drive output current.
I have had good history with Lenze SMVector drives as a cheaper unit compared to our company standard of using all Rockwell/AB drives ($$$$). Others mfrs may be cheaper than Lenze, but I have no working experience/history with any others.

Post a pic of the motor nameplate.

Is your only purpose for the drive to get a 3 phase input from a single phase source or do you need other features?
I only think you may need 3 wire control (stop/start pb's/low voltage drop out) and accel ramp feature for a gentler "soft start".
 
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
Typical specs refer to drive output current.
I have had good history with Lenze SMVector drives as a cheaper unit compared to our company standard of using all Rockwell/AB drives ($$$$). Others mfrs may be cheaper than Lenze, but I have no working experience/history with any others.

Post a pic of the motor nameplate.

Is your only purpose for the drive to get a 3 phase input from a single phase source or do you need other features?
I only think you may need 3 wire control (stop/start pb's/low voltage drop out) and accel ramp feature for a gentler "soft start".

I dont have the jointer yet, picking it up monday.

I am right now only concerned about getting it to run, yes 1 phase to 3 phase. I dont know about the other items, i will have to go with advice from others.

Thanks
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,485
Rotary Phase Converter is another option that you might want to look at for a jointer. Or just swap moter with a single phase if just one machine. VFC gives a lot of nice options such as slow start/stop, variable speed and fwd/rev that you may not need for jointer.
 
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
Rotary Phase Converter is another option that you might want to look at for a jointer. Or just swap moter with a single phase if just one machine. VFC gives a lot of nice options such as slow start/stop, variable speed and fwd/rev that you may not need for jointer.

I am considering a swap out, it seems a VFD is cheaper, and would keep the machine original.

Rotary Phase Converter are too expensive.

Bells and whistles are great, I just need to know if the meat and potatoes part of the VFD will work first.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,313
Location
NJ
I dont have the jointer yet, picking it up monday.

I am right now only concerned about getting it to run, yes 1 phase to 3 phase. I dont know about the other items, i will have to go with advice from others.

Thanks

Make sure it runs before you own it. I assume you have 3 phase power at the seller's location.
Then post n/p.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,485
If you want cheap you could run it with another 3ph motor and piece of rope lol. 3ph motors are a dime a dozen (used).
 
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
If you want cheap you could run it with another 3ph motor and piece of rope lol. 3ph motors are a dime a dozen (used).

Im not sure I understand, I already have 3ph motor, and need it to run on 1 ph.

A VFD seems a sensible option, i see many use them.

The more i research, it seems a 3hp 3phase motor draws about 9.6 amps, so the VFD at 10.5 should suffice. I am going to email the mfg of the VFD to to confirm.

Thanks!
 
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
Make sure it runs before you own it. I assume you have 3 phase power at the seller's location.
Then post n/p.

Im buying it blind, so I wont get to run it. At the price I am getting it for, even if I do have to buy a new motor, I am still well ahead.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,485
You can use another 3ph motor wired to single phase 220 to generate third leg for your jointer. RPC use circuitry to start the motor but you can get motor running by getting it spinning (by rope or another small 120v motor) and applying power to it. At that point you have 3 pH being generated by the free running motor which you can use to run other 3ph equipment. The free running motor needs to be about 50% larger than your equipment. I bought a used 7.5hp Baldor motor for $100 and its a monster. I also bought the caps and relays to have it self start. There are tons of videos on YouTube showing how to do it. With that said if you only have the one machine VFD may be way to go. Just throwing out other options for you. Good luck.
 
OP
G

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
You can use another 3ph motor wired to single phase 220 to generate third leg for your jointer. RPC use circuitry to start the motor but you can get motor running by getting it spinning (by rope or another small 120v motor) and applying power to it. At that point you have 3 pH being generated by the free running motor which you can use to run other 3ph equipment. The free running motor needs to be about 50% larger than your equipment. I bought a used 7.5hp Baldor motor for $100 and its a monster. I also bought the caps and relays to have it self start. There are tons of videos on YouTube showing how to do it. With that said if you only have the one machine VFD may be way to go. Just throwing out other options for you. Good luck.

Ok, never knew that.

Yes, for the one machine, I am going with VFD.

I think I have settled on this one:

http://dealerselectric.com/FM50-203-C.asp?gclid=CLyohdGql9ICFYk8gQodkkQFJw

Thanks for everyones help!
 
To avoid these ads, REGISTER NOW!

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,485
Teco is about the best out there before you start getting into real money. I bought that same one for a drill press but haven't used it yet. Had good reviews.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
often times you will need a larger unit to make the conversion from 1ph to 3ph. make sure you read the specs on that before you buy the drive
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,822
Location
SE Michigan
As Jason says, you need to investigate the "derating" factor of the VFD for using single phase input as opposed to 3ph input. Its somewhere in the thick manual.

The power side wiring is a snap, 2 (or 3) wires in and 3 out to the motor.

Now you have to decipher the control wiring, it can be either 2-wire with a maintained switch like a wall-toggle switch or it can be a 3-wire spring return start and stop pushbutton station. Wiring for this plus possibly a parameter change.

The hardest part is going thru all the parameters to see what you need, there's an array of like 100 different parameters because the thing can be installed in innumerable ways. It can have set speed, it can have discrete speed steps, it can have variable speed, the speed reference can come from the front of the panel up and down arrows, it can be a remote potentiometer, it can be network-transferred over from a PLC...just to give you a very small window into how they can be applied.

Just ask questions if you get stuck :) we can help.
 
Last edited:

rsanter

Well-known member
Joined
Dec 22, 2007
Messages
18,556
Location
visalia ca
I prefer the VFD, however you can basically make your own rotary phase converter if you have another three phase motor that is slightly larger that the motors you want to run.
buy a static converter for say a spare 5ph 3phase motor. then you run the motors you want in the equipment off of the 5hp 'rotary phase converter' that you created. basically it just self gens the third leg and adsorbs the losses of going 1phase to 3phase

I did this for years with my lathe and mill. the lathe was 3hp and had a static converter, the mill was 1hp so I connected the wires for the mill motor to the lathe motor. take the lathe out of gear (ideling) and turn the mill on.
worked great for no extra money. now both are on their own VFDs

bob
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,313
Location
NJ
matt_i;6322178[B said:
]As Jason says, you need to investigate the "derating" factor of the VFD for using single phase input as opposed to 3ph input.[/B] Its somewhere in the thick manual.

The power side wiring is a snap, 2 (or 3) wires in and 3 out to the motor.

Now you have to decipher the control wiring, it can be either 2-wire with a maintained switch like a wall-toggle switch or it can be a 3-wire spring return start and stop pushbutton station. Wiring for this plus possibly a parameter change.

The hardest part is going thru all the parameters to see what you need, there's an array of like 100 different parameters because the thing can be installed in innumerable ways. It can have set speed, it can have discrete speed steps, it can have variable speed, the speed reference can come from the front of the panel up and down arrows, it can be a remote potentiometer, it can be network-transferred over from a PLC...just to give you a very small window into how they can be applied.

Just ask questions if you get stuck :) we can help.

The drive that OP linked to is 3HP for either single phase or 3 phase.

For 3 wire control it looks like he will need an external relay to seal around itself if he wants 3 wire control.

Only 30 parameters!

OP, make sure your 3 phase motor can be wired to 240 vac. You can't get 480 out of this drive.

You may want to consider the NEMA4 (IP65) enclosure option and be done with the entire need for another enclosure to keep dust out.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
A single phase input VFD does not have to be derated, and 3 HP & smaller drives are pretty reasonable.
 

JoelPNellis

New member
Joined
Sep 16, 2019
Messages
2
Location
Pittsburgh
Can anyone give me a hand on wiring my VFD? I have a single phase to single phase VFD for adjusting the speed of an exhaust blower. Instructions talk about the main winding and secondary winding, but my wiring diagram on my motor only has A PHASE and B PHASE. Anyone have any idea how this should go?fullsizeoutput_4245.jpegfullsizeoutput_4242.jpg
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
VFD’s are for 3 phase motors only, some drives are made for or can run on a single phase supply but the output is 3 phase.
 

JoelPNellis

New member
Joined
Sep 16, 2019
Messages
2
Location
Pittsburgh
Here is the Single Phase VFD I am using ato.com/10hp-vfd-single-phase-input-output. The company is ATO in Diamond Bar, CA. It is designed for single-phase motors, but I'm having difficult figuring out the wiring of my motor to connect it properly.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,021
Location
East Cobb County, Georgia
Looks like it is a 3 phase output, but they wire it to the start and run windings of a single phase motor and eliminate the capacitors because the drive provides the needed phase shift. I think we could figure it out, but suggest you contact the manufacturer for tech support.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
Can anyone give me a hand on wiring my VFD? I have a single phase to single phase VFD for adjusting the speed of an exhaust blower. Instructions talk about the main winding and secondary winding, but my wiring diagram on my motor only has A PHASE and B PHASE. Anyone have any idea how this should go?fullsizeoutput_4245.jpegfullsizeoutput_4242.jpg

looks like you already have the wiring diagram for the motor.

you would need to remove the capacitor and connect primary and secondary windings as shown in the second pic.

make sure to get the rotation correct.
 