Put up a link to the VFD you're looking at - typically they are rated by their output current, but it will be easier to give a good answer if we can see the specifications.
Typical specs refer to drive output current.
I have had good history with Lenze SMVector drives as a cheaper unit compared to our company standard of using all Rockwell/AB drives ($$$$). Others mfrs may be cheaper than Lenze, but I have no working experience/history with any others.
Post a pic of the motor nameplate.
Is your only purpose for the drive to get a 3 phase input from a single phase source or do you need other features?
I only think you may need 3 wire control (stop/start pb's/low voltage drop out) and accel ramp feature for a gentler "soft start".
Rotary Phase Converter is another option that you might want to look at for a jointer. Or just swap moter with a single phase if just one machine. VFC gives a lot of nice options such as slow start/stop, variable speed and fwd/rev that you may not need for jointer.
I dont have the jointer yet, picking it up monday.
I am right now only concerned about getting it to run, yes 1 phase to 3 phase. I dont know about the other items, i will have to go with advice from others.
Thanks
If you want cheap you could run it with another 3ph motor and piece of rope lol. 3ph motors are a dime a dozen (used).
Make sure it runs before you own it. I assume you have 3 phase power at the seller's location.
Then post n/p.
You can use another 3ph motor wired to single phase 220 to generate third leg for your jointer. RPC use circuitry to start the motor but you can get motor running by getting it spinning (by rope or another small 120v motor) and applying power to it. At that point you have 3 pH being generated by the free running motor which you can use to run other 3ph equipment. The free running motor needs to be about 50% larger than your equipment. I bought a used 7.5hp Baldor motor for $100 and its a monster. I also bought the caps and relays to have it self start. There are tons of videos on YouTube showing how to do it. With that said if you only have the one machine VFD may be way to go. Just throwing out other options for you. Good luck.
matt_i;6322178[B said:]As Jason says, you need to investigate the "derating" factor of the VFD for using single phase input as opposed to 3ph input.[/B] Its somewhere in the thick manual.
The power side wiring is a snap, 2 (or 3) wires in and 3 out to the motor.
Now you have to decipher the control wiring, it can be either 2-wire with a maintained switch like a wall-toggle switch or it can be a 3-wire spring return start and stop pushbutton station. Wiring for this plus possibly a parameter change.
The hardest part is going thru all the parameters to see what you need, there's an array of like 100 different parameters because the thing can be installed in innumerable ways. It can have set speed, it can have discrete speed steps, it can have variable speed, the speed reference can come from the front of the panel up and down arrows, it can be a remote potentiometer, it can be network-transferred over from a PLC...just to give you a very small window into how they can be applied.
Just ask questions if you get stuckwe can help.


Can anyone give me a hand on wiring my VFD? I have a single phase to single phase VFD for adjusting the speed of an exhaust blower. Instructions talk about the main winding and secondary winding, but my wiring diagram on my motor only has A PHASE and B PHASE. Anyone have any idea how this should go?![]()