Water Heater Install

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
Hi all:

I'm replacing a gas water heater with an electric one. The plan is to run 10/2 NM-B from a 30 amp breaker in an existing exterior-mounted panel, through 3/4" PVC conduit up the side of the two-story house into the eave, over the rafters in the attic, and then down through a hole in the sheetrock in the water heater closet on the 2nd floor. I'd planned to "hardwire" the Romex directly to the short wires coming out of the water heater inside the little door on top of the heater.

However, does NEC 2011 422.31(B) require a disconnect within reach? IF so, does this work?

Or does the little lock tab on the exterior panel count as "being locked in the open position"?

Thanks!
 
To avoid these ads, REGISTER NOW!

gregtwojeeps

Well-known member
Joined
Jul 30, 2013
Messages
5,096
Location
Ky
The little 30 amp two pole disconnects at the box stores are cheap enough. I would be sure the safety of anyone possibly needing to work on the heater is assured, by putting it on the wall by the heater. I used a cord/plug means of disconnect on my WH, but so that I could move the WH power cord from the KU power outlet over to my generator power outlet as needed. good luck
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
What is a KU power outlet? Is this a code name for something that has a meaning only to you?

The little 30 amp two pole disconnects at the box stores are cheap enough. I would be sure the safety of anyone possibly needing to work on the heater is assured, by putting it on the wall by the heater. I used a cord/plug means of disconnect on my WH, but so that I could move the WH power cord from the KU power outlet over to my generator power outlet as needed. good luck
 
OP
D

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
Looks like that link didn't work. Here it is: 60 amp

782114103234.jpg


They have a 30 amp one too, but its more expensive....
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That will work fine as a disconnect.

I don't know what the deal is with posting a link to a Lowes page. I have had the same problem with it showing a general page and not what I copied and pasted.


Looks like that link didn't work. Here it is: 60 amp

....
 

gregtwojeeps

Well-known member
Joined
Jul 30, 2013
Messages
5,096
Location
Ky
What is a KU power outlet? Is this a code name for something that has a meaning only to you?

Nothing fancy, KU = Kentucky Utilities is my home power supplier. I meant my WH has a outlet in the house powered by KU power. I have two female 30 A - 250 rated outlets at my WH, one stacked above the other. The KU outlet above, gen powered oulet below. Sorry for the confusion...
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
OK thanks. Will the lock tab on the panel not suffice?

Code will require a disconnect in sight of, and within 50 ft of the equipment. It only makes sense. If you are running conduit all the way to the closet where the WH is located, don't use Romex, but rather, measure and buy individual THHN wires. They are MUCH easier to pull thru the conduit. You will be quickly hating yourself if you try to pull Romex that far in conduit.

Charles
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Hi all:

I'm replacing a gas water heater with an electric one. The plan is to run 10/2 NM-B from a 30 amp breaker in an existing exterior-mounted panel, through 3/4" PVC conduit up the side of the two-story house into the eave, over the rafters in the attic, and then down through a hole in the sheetrock in the water heater closet on the 2nd floor.

What is the total length of that wiring run, end to end? If it is more than about 90 feet, AWG 10 is going to be marginal, at best. Yes, it will still be "legal"; but voltage drop will start to rear its ugly head.

Also, I agree with Charles: If you're going to be installing a full run of conduit anyway, go with individual wires, not NM-B, for the entire run. If OTOH you're only planning to use the conduit to protect the "exposed" portions of the run, then put a junction box just inside the attic (and maybe another one just above that closet ceiling), and make the THHN/NM-B transition(s) there.

Finally, just out of curiosity: Why are you converting from gas to electric? The former will surely be far less expensive to feed over the long haul.

 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
You can't run NM-b in conduit outside, its a wet location, have to be 10-2 uf
 
To avoid these ads, REGISTER NOW!

porschedude996TT

Well-known member
Joined
Oct 28, 2007
Messages
2,384
Location
Santa Maria, California
Wow, can you tell us why you need to change to an electric water heater? From my location, where gas is cheap-cheap-cheap, and electricity is not federally funded by an antiquated law, it does not make sense to change from natural gas to electric. Was your old water heater propane fueled?
 
OP
D

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
It wasn't my place (I have gas). Around here both the gas and electric utilities will provide a free replacement water heater to switch from one to the other plus cash for the install.

The old gas unit was rusted and leaking.
 

borgdog

Well-known member
Joined
Jan 8, 2011
Messages
109
Location
Spokane, WA
It wasn't my place (I have gas). Around here both the gas and electric utilities will provide a free replacement water heater to switch from one to the other plus cash for the install.

The old gas unit was rusted and leaking.

:lol_hitti So when you need a water heater you just switch from one to the other and get it for free. Nice.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
It wasn't my place (I have gas). Around here both the gas and electric utilities will provide a free replacement water heater to switch from one to the other plus cash for the install.

The old gas unit was rusted and leaking.

Man, where do u live? never heard of a utility paying to replace a water heater!

I would have put in another gas WH. NG is way more efficient than electric!
 
Last edited:

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
It is true that a NG water heater is not as efficient as an electric unit. The electric unit is 100% efficient and NG is something less than that depending on what it is. However, the savings comes from energy costs. In my area, I can heat 3 to 4 gallons of water with NG for the cost of heating one gallon with electricity.
 