Yeah, it's weird. I was installing a dimmer in a switched box. This is not the switch box, it is switched up the line. Only two wires into the box. Apparently the rigid conduit is being used as the ground for now.
So here's the weirdness: I plugged in a light, made sure the switch was in the 'off' position and proceeded when I got bit. So, I checked with my touchless and there was a hot somewhere. (Now before you go and tell me, yeah, I slipped and didn't do my due diligence which is a reminder to all, always test, test, test.)
I carefully rigged up a temporary receptacle and plugged in my 3 light tester. I grounded the recep to the box. With the switch off, I showed hot/neutral rev.
With the switch on I showed hot/ground rev. So I got out my Wiggy and did more. Sure enough, neutral to ground lit up in "off" switch position and hot to ground in the "on" position.
OK, sorry this is long and I know the dimmer acts as a switch itself. In this case we just wanted a dimmer for one of the lights on that switched circuit and the others at full bright. So the dimmer was going to be set and left alone while the circuit it is on would remain switched from another location. No other way to place a dimmer as the device is a chandelier and the switch leg is in a j-box that I can use for this dimmer. The other lights will be pigtailed to the line side.
I didn't have time to go any further so I closed everything up and left the job as I found it and the lights all still work. Obviously I'm going to get this straighten out ASAP.
You want even more weird? I did put my Wiggy on the switch lugs and guess what? No power across the lugs from line to switched when on. But I had power at the switched side when the switch was in the "off" position. So I came home baffled.
Summary of switching: Off, I have power between white and green. On, I have power between black and green. No other combos work; no power to white while "on". Conduit is the same as 'green'.
WTF?
So here's the weirdness: I plugged in a light, made sure the switch was in the 'off' position and proceeded when I got bit. So, I checked with my touchless and there was a hot somewhere. (Now before you go and tell me, yeah, I slipped and didn't do my due diligence which is a reminder to all, always test, test, test.)
I carefully rigged up a temporary receptacle and plugged in my 3 light tester. I grounded the recep to the box. With the switch off, I showed hot/neutral rev.
With the switch on I showed hot/ground rev. So I got out my Wiggy and did more. Sure enough, neutral to ground lit up in "off" switch position and hot to ground in the "on" position.
OK, sorry this is long and I know the dimmer acts as a switch itself. In this case we just wanted a dimmer for one of the lights on that switched circuit and the others at full bright. So the dimmer was going to be set and left alone while the circuit it is on would remain switched from another location. No other way to place a dimmer as the device is a chandelier and the switch leg is in a j-box that I can use for this dimmer. The other lights will be pigtailed to the line side.
I didn't have time to go any further so I closed everything up and left the job as I found it and the lights all still work. Obviously I'm going to get this straighten out ASAP.
You want even more weird? I did put my Wiggy on the switch lugs and guess what? No power across the lugs from line to switched when on. But I had power at the switched side when the switch was in the "off" position. So I came home baffled.
Summary of switching: Off, I have power between white and green. On, I have power between black and green. No other combos work; no power to white while "on". Conduit is the same as 'green'.
WTF?