Welder tripping other breakers...weird

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
Howdy all, I have a problem that is perplexing me to no end. My garage has a single 120v duplex outlet, on its own 20a breaker, that I use for my 120v welders. Recently I picked up the new HF Titanium Flux 125, and while it is a great little welder, it trips the breakers (AFCIs I believe) on totally different circuits. The moment I strike the arc the breaker for the upstairs trips and my wife’s computer shuts down. It has also tripped the breaker for my shop lights. All the while the welder is still chugging along. How on earth is it tripping totally different circuits? My other two 120v welders don’t cause a problem even cranked all the way up. The new welder trips those other circuits even when turned way down on output power.

I know that AFCIs are supposed to detect weirdo fluctuations in arcing or what have you, but on a different circuit? I don’t get it. Could the inverter welder be causing some sort of RF interference that is tripping the breakers?

Any help would be appreciated...

Ken
 
To avoid these ads, REGISTER NOW!

BigGarage

Well-known member
Joined
Jun 5, 2019
Messages
2,344
Location
Just south of Detroit, MI.
Howdy all, I have a problem that is perplexing me to no end. My garage has a single 120v duplex outlet, on its own 20a breaker, that I use for my 120v welders. Recently I picked up the new HF Titanium Flux 125, and while it is a great little welder, it trips the breakers (AFCIs I believe) on totally different circuits. The moment I strike the arc the breaker for the upstairs trips and my wifeÂ’s computer shuts down. It has also tripped the breaker for my shop lights. All the while the welder is still chugging along. How on earth is it tripping totally different circuits? My other two 120v welders donÂ’t cause a problem even cranked all the way up. The new welder trips those other circuits even when turned way down on output power.

I know that AFCIs are supposed to detect weirdo fluctuations in arcing or what have you, but on a different circuit? I donÂ’t get it. Could the inverter welder be causing some sort of RF interference that is tripping the breakers?

Any help would be appreciated...

Ken
I'll tell you what's really weird; those little "up" arrows over a capital "A".:).
I cannot help with your situation though, sorry.

EDIT: I found this online.

As far as the AFCI tripping when a "high load" comes on "any circuit"--could indeed be a bad ACFI breaker, as Hiker mentioned. Or it could be some miswire or fault in the system. If anothter AFCI breaker does the same thing, I suggest not ignoring it and swapping the AFCI out for a standard breaker. There's something wrong, and although the system may function, it'd be prudent to find out what the problem is.

Time to call in a pro, someone with real troubleshooting skills (and when I say that, I don't mean to diss Hiker...) If there's some weird fault, it may take some time (and time = money) to find it.

That's the thing about these AFCIs. They trip under conditions that we never would have known about before...like neutral/equipment ground crosses, or inadvertantly shared neutrals between circuits. Or more seriously, there may be a high-impedance ground fault, or short somewhere. And finding something like that before it goes south is a good thing.



Dennis
 
Last edited:

gungatim

Well-known member
Joined
Jan 8, 2013
Messages
8,101
Location
west mich
Spurious RF emissions can set off some brands of AFCI breakers. would not be surprised if the circuit in low cost welders are not shielded...
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,524
Location
VT
There's other threads about this issue.

I have had my Lincoln trip gfci on different circuits.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I would think maybe it has something with the neutral connections. But if they got mixed up when the place was wired, they would do it when you would plug anything in. Are these circuits that tripping all on the same phase/leg?
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Just curious, what brand panel/afci's do you have?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I did try to look it up on the internet. It seems that it could possibly be a frequency issue caused by the welder. Its beyond my knowledge.
 

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,818
Location
(rural) Maryland
It is likely due to the welder emitting high frequency EMI, which can trip GFCIs and AFCIs, even if they aren't on the same circuit. If there is a high frequency start option try turning it off. Other than that, you can only try to ground the machine better or try replacing the breakers as you might have gotten a few that were extra sensitive. Last resort, see if Harbor Freight will swap it out.
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
Alright, so an update... but first, thanks for all the input and ideas. On a whim I connected the welder to my generator and ran it off of that to see if it was a wiring thing in the box. Figured if it was RF interference the circuits would still trip. Went for the gusto on full power and... nothing. No AFCIs tripped. Tried repeatedly and nada. Plugged welder back in to the regular circuit, hit the gas and...nada, no AFCIs tripped. Aaargh! At this point I’m going with the assertion that AFCIs are haunted :)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
wait a minute

you have a cutler hammer panel with tan handle breakers and BR AFCIs?

I dont think BR AFCIs are listed for use in a CH panel. BR breakers are for use in a BR panel.

There are AFCIs listed for use in CH panels.

https://www.amazon.com/dp/B00AQ9NGJM/?tag=atomicindus08-20

Cutler hammer has 2 lines, the BR which actually stands for Bryant whom the bought out years ago. And the CH line. Eaton owns them now. There is no way to swap the 2 breakers. defiantly not interchangeable. Its like trying to put a QO breaker in a Homeline panel.
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Nope, just GFCI protection on the receptacles

In the 2017 edition of the NEC®, Section 210.12 requires that for dwelling units, all 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by AFCIs.

Sent from my SM-G960U using The Garage Journal mobile app
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
AFAIK...

AFCIs have a processor that looks at high frequency 'content' in the circuit, to try and identify the distinctive characteristics of an 'arc' fault.

The HF (and other) welder apparently is generating enough noise in the circuit (and back the the panel) that the AFCIs are seeing it....
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
Thanks again for all of the ideas and input. I’m kind of glad that my first thought of RF interference (or otherwise) might have been the culprit. Everything got stranger of course when I couldn’t duplicate the problem using power from the generator (which may have cancelled out the RF interference) or when plugging the welder back in to the wall outlet.

Today I picked up another HF Flux 125 and will experiment to see if it was a fluke. If the AFCIs have microprocessors then I may never figure out the catalyst that causes a false signal and trips the random breakers. I don’t want the solution to be replacing AFCIs with standard breakers just in case, and the resulting fire investigation. What about some kind of line filter for the welder power cord? Installing $400 worth of different AFCIs would be a bummer and no way am I taking the easy route of getting a different welder.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Thanks again for all of the ideas and input. I’m kind of glad that my first thought of RF interference (or otherwise) might have been the culprit. Everything got stranger of course when I couldn’t duplicate the problem using power from the generator (which may have cancelled out the RF interference) or when plugging the welder back in to the wall outlet.

Today I picked up another HF Flux 125 and will experiment to see if it was a fluke. If the AFCIs have microprocessors then I may never figure out the catalyst that causes a false signal and trips the random breakers. I don’t want the solution to be replacing AFCIs with standard breakers just in case, and the resulting fire investigation. What about some kind of line filter for the welder power cord? Installing $400 worth of different AFCIs would be a bummer and no way am I taking the easy route of getting a different welder.

FYI- the BR AFCIs you have are not listed for use in the CH panel you have. They should be hanged regardless of yhe welder
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Wylies, he has to have a BR panel. There is no way possible to put a BR breaker in a CH panel. The breakers are different thicknesses and attach to the buss completely different CH is first picture, BR is second

Sent from my SM-G960U using The Garage Journal mobile app
 

Attachments

  • s-l1600.jpg
    s-l1600.jpg
    99.4 KB · Views: 13
  • 100170174_S01_R01_C12.jpg
    100170174_S01_R01_C12.jpg
    29.6 KB · Views: 11
Last edited:

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,967
Location
Peace Valley,mo
Alot of weird electrical problems are from a bad ground. Since the problem is about induced noise or frequency and not line voltage the ground connection might be good for voltage but not the other. Ground rod connections normally just clamped to rod and a clean connection might help.
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Since that machine is an inverter it might be causing a harmonic. At that price point I doubt they've spent much, if anything, on filtering.
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
I can certainly give that a shot, so you’re talking about the ground rod next to the house right? Anything special I need to do before messing with that, breaker wise?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Alot of weird electrical problems are from a bad ground. Since the problem is about induced noise or frequency and not line voltage the ground connection might be good for voltage but not the other. Ground rod connections normally just clamped to rod and a clean connection might help.

Ummm no

Under normal operation, no voltage/current flows on grounding electrodes.

Grounding electrodes are for shunting lightening, limiting voltage to earth potential, and shunting primary voltage when it comes into contact with secondary lines.

Stray Currents and harmonics do not return to earth, despite popular misconcetion, they return to the source. The earth is not a good conductor for stray currents.

A ground rod is not gonna disipate what you describe.

Stray harmonics will return to the transformer via the neutral or hot legs.

Many transformers have been blown due to high harmonics induced by customer equipment.

A ground rod will not transmit these back to the transformer via earth
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
I can certainly give that a shot, so you’re talking about the ground rod next to the house right? Anything special I need to do before messing with that, breaker wise?

Turn the main off. The ground can go hot when you disconnect it from the grounding rod:shocking:
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
The more I think about it, the more it seems like RF interference or the like. There’s no way the welder is drawing too many amps, my dust collector pulls way more on startup. I picked up another welder of the same model (Black Friday sale :) and still need to hook it up and see what happens. Maybe the one I have has a weird component or wire touching something that is causing the problem.
 

SGKent

Banned
Joined
Feb 12, 2010
Messages
1,959
Location
Citrus Heights CA
is there another 20 amp circuit you can plug it into and see if it trips other breakers? If it continues then my thought is that there is a problem with the neutral bus that is causing it to rise in voltage for a brief moment, which fools the other breakers into thinking they have a fault. Might be time to ask the electric company to check all 3 legs to see if there is any corrosion in one of them. It does happen.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
My first thought is poor connections in neutrals. My first action would be to clean all the neutral connections in the panel, and make sure they're torqued properly.
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
My first thought is poor connections in neutrals. My first action would be to clean all the neutral connections in the panel, and make sure they're torqued properly.

I’m following, but the two offending AFCIs don’t trip with my other two 120v welders even when set at max (80-125a) output. The inverter flux mig trips those two AFCIs even when turned down (40a or so), but doesn’t trip it’s own 20a standard breaker.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I’m following, but the two offending AFCIs don’t trip with my other two 120v welders even when set at max (80-125a) output. The inverter flux mig trips those two AFCIs even when turned down (40a or so), but doesn’t trip it’s own 20a standard breaker.

I'm definitely guessing, I'm an automotive guy. Whenever a car has one circuit affecting another, the first place to look is the grounds, which is analogous to the neutrals in house wiring. Factor in all the connections in the panel and the fact you're actually making arcs - and who knows what frequencies make the breakers trip.
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,774
Location
Southern Oregon
Possibly the proximity of the cables, sort of like phantom voltage. IOW, the cables run closely along side each other for a distance and that's inducing the arc frequency into the cables going to the AFCI breakers.
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,931
Location
Shepheardsville, KY
How about checking the MFG web site to see if anyone else is experiencing the same problem, OR is there a product recall on those breakers ???
 

472scout

Well-known member
Joined
Sep 18, 2010
Messages
1,276
Location
back 40
I had a similar issue with breakers tripping randomly and during lightning storms. It turned out to be a broken wire on a 15 amp circuit in the main panel. The wire was completely broke through, but the ends were touching. If this was my house I would stick a circuit tester into every outlet to verify proper wiring, visually and manually check every connection and wire in the panel, and then break out the multimeter and test suspect circuits. Tons of youtube videos on how to do that. Be careful.
 
OP
N

Neuhaus

Member
Joined
Nov 26, 2019
Messages
9
Location
North Carolina
Another update; I hooked up and ran the second HF Titanium Flux 125 with no issues. I ran bead after bead on different power settings and neither of the two haunted AFCIs tripped. A couple of people had suggested cleaning and or tightening down the neutrals in the breaker box and it didn’t quite make sense to me in that I couldn’t see how this particular welder would be affected by a wonky neutral wire but not other high draw tools plugged in to that same outlet. Maybe something was awry in that particular unit, or there were other conditions that added up to an RF interference when I pulled the trigger on the mig gun and popped one of those two AFCIs. I’ll have to run the new welder some more and see if it happens again. Thanks again for the input and suggestions :)
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
whats the wiring in the panel look like? are the wires for the "welder" circuit nice and tidy or wrapped over/under around other stuff in the panel?
 