Well here’s a new issue...

grizzlebar

Well-known member
Joined
Jan 14, 2016
Messages
93
New construction house about 7 months old, installed 2 Nest thermostats on a 2 zone system (one compressor and one handler). No issues until now (at least that I’ve noticed)

So I was downstairs and walked through the main hallway which I thought was quite warm - looks like there is warm air coming out of my return intake.

Made my way upstairs to check the other one, which is drawing air in just fine and pushing it out to all the upstairs vents.

Thinking i was crazy, came back down and verified - no air is coming out of the supply vents, but it is coming out of the return intake...


Thoughts?
 
To avoid these ads, REGISTER NOW!

Done That

Well-known member
Joined
Aug 18, 2017
Messages
601
Location
MO
Does the system have zone dampers in the ductwork?
All I can think is a mostly/completely blocked supply so air is "backflowing"...but i'd think it would trip a limit super fast??? Weird....
 
OP
G

grizzlebar

Well-known member
Joined
Jan 14, 2016
Messages
93
So I’m pretty the supply/return main lines got mixed up when everything was put together. Only thing I can think of that explains full outflow at the return vent.

I guess I never noticed it before...
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,310
Location
Dutzow Missouri
If only one zone is calling for heat the system may be setup to dump any excess air pressure into the return system and some air may escape a nearby register

Walta
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Is it variable speed --- how is the system controlling the zones?

It could have a bypass if the system has no other way to balance
 
OP
G

grizzlebar

Well-known member
Joined
Jan 14, 2016
Messages
93
Even turning off the upper zone it still happens. My money is on crossed lines.
 
OP
G

grizzlebar

Well-known member
Joined
Jan 14, 2016
Messages
93
10aa8552a44167b0c44cb344bfa99f09.jpg
 
Last edited:

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
So I’m pretty the supply/return main lines got mixed up when everything was put together. Only thing I can think of that explains full outflow at the return vent.

I guess I never noticed it before...

System has been commissioned and running 7 months. Wierdness recently noticed. I'd bank on a zone damper issue before assuming supply/return ducts crossed up...

Made a joke with the Nest Tstats. They are finicky at times. Like they are self aware, which they are.

Are the Nest's controlling the system? The zoning? Have a zone controller? Need more info.

CT
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I'm assuming it's must be a 3rd party zone system. All the recent manufacturer zone controls require manufacturer specific thermostats.

OP should take some pictures of the system and look at the zone controllers to make sure they are operating
 
To avoid these ads, REGISTER NOW!

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
I'm assuming it's must be a 3rd party zone system. All the recent manufacturer zone controls require manufacturer specific thermostats.

OP should take some pictures of the system and look at the zone controllers to make sure they are operating

This is why I made the Nest statement earlier... Universal tstats and zoning don't always play nice.

CT
 
OP
G

grizzlebar

Well-known member
Joined
Jan 14, 2016
Messages
93
AC guy came out - supply and return lines were crossed during installation
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
So I’m pretty the supply/return main lines got mixed up when everything was put together. Only thing I can think of that explains full outflow at the return vent.

I guess I never noticed it before...

That is the only thing it can be. Changing the stat would not change airflow direction, even with malfunctioning zone dampers.

Tommy
 