What is it? Buss Fuse in socket.

geojag

Well-known member
Joined
Oct 11, 2012
Messages
359
Location
Little Rock, AR
I have been looking at houses recently, and in a couple houses I have seen a single socket with a screw in Buss Fuse and what appears to be a capacitor. In both cases the houses were reportedly built in the 1970s and have a regular breaker box as well. A picture is attached. Any help is appreciated!

cfe8ee72c96ac795dff3f02606cf4ba4.jpg


Sent from my Pixel XL using Tapatalk
 
To avoid these ads, REGISTER NOW!

ABSTIFFGS

Well-known member
Joined
Feb 4, 2014
Messages
304
Location
Twin Cities, MN
That to me looks like a doorbell transformer. Could they have used the light bulb base as a "fuse holder" to protect the transformer?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,745
Location
NW Iowa
I would assume it's additional protection for the doorbell or HVAC transformer that is visible on the side of the box.

A porcelain lamp holder isn't really the right thing for this but I wouldn't get worried about it either since it's a 3 amp fuse...
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,745
Location
NW Iowa
It's not uncommon to use small fuses like this to provide additional protection to small loads since 15a is pretty much the smallest common breaker.

Most doorbell transformers have an internal fuse but this one may not, thus the plug fuse.
 
OP
G

geojag

Well-known member
Joined
Oct 11, 2012
Messages
359
Location
Little Rock, AR
Thanks for the answers. I had initially thought it was doorbell related, but the location and the fuse threw me. I guess the just put it in closets to make them accessible but out if sight.

Sent from my Pixel XL using Tapatalk
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
I guess the just put it in closets to make them accessible but out if sight.

It's a Code violation then
NEC 240.24
(D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,745
Location
NW Iowa
It's a Code violation then
NEC 240.24
(D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.

Nobody said it was a clothes closet...
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Nobody said it was a clothes closet...

I don't think it really matters what type of closet, what does matter is closets are used for storage & likely contain material that is easily ignitable.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
Nobody said it was a clothes closet...

If the wall has wood framing, it's also a violation of this one.

(A) Not over 112-1⁄2 kVA. Dry-type transformers installed indoors and rated 112-1⁄2 kVA or less shall have a separation of at least 300 mm (12 in.) from combustible material unless separated from the combustible material by fireresistant, heat-insulated barrier.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,745
Location
NW Iowa
If the wall has wood framing, it's also a violation of this one.

(A) Not over 112-1⁄2 kVA. Dry-type transformers installed indoors and rated 112-1⁄2 kVA or less shall have a separation of at least 300 mm (12 in.) from combustible material unless separated from the combustible material by fireresistant, heat-insulated barrier.

You got a code section for that? I wouldn't mind reading the whole article.
 