Corbin5754
Well-known member
You would use a 60amp double pole breaker in the house if that's what you want in the shop. You could then install a 100 amp (or 200 amp, or anything 60amp or greater) panel in the shop with no problem. The 100 amp breaker in the shop panel would just serve as a disconnect, as you would be limited to the 60amp supplied from the house.
Thank you. So my plan is to run the 2-2-2-4 mhf wire in conduit underground and drill a hole into crawl space and run wire to main box which will be about 8 feet from the drilled hole . Now after the wire gets under house do I still have to run conduit all the way to box? If so I'd like to run a wire that doesn't require conduit all the way to the box.