Kinda irrelevant since I (homeowner) figured out and fixed the problem but wondering general opinion of the pro's as to who's problem this is/was?

Recently completed garage expansion. As part of it, all new subpanel and everything feeds into that. As part of it, I had the electrician add an outside disconnect and 30 amp 220 circuit to have a split a/c unit installed afterwards. Fast forward a few weeks, hvac friend shows up and installs daikin 24k mini split. And... line side has 240v, no power coming out of the load side of the disconnect. hvac guy talks to electrician, both conclude disconnect is bad, sparky says he will stop by following week to replace it. Never shows....

I pulled the entire thing off the wall, took it apart, no continuity across anything. Google search show me apparently there are supposed to be 2 fuses installed on the back side of the puller. Neither of them ever thought to ask about it when they talked 2 weeks ago...

Is this something the electrician should have added? The hvac guy? Heading to HD to pick up the fuses shortly, just wondering for my own sanity... very disappointed that NEITHER of them thought to check/look and it takes me, a ******* homeowner, to figure out what the problem is.
 
To avoid these ads, REGISTER NOW!

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,360
I'd just be happy it's an easy fix but a bit concerning that neither one thought to look for fuses if this is a common disconnect (I have no clue). Glad you got it resolved. This is a good example of why I strongly prefer doing my own work whenever possible.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,296
Location
Illinois near St. Louis, Missouri
Crazy that neither of them figured out the fuses were missing. I tend to think the HVAC guy is responsible. A lot of disconnects don't include fuses so wondering why the electrician put that in. Maybe it was just what was on the truck. Frustrating I know - you expect them to know more than a weekend warrior. But at least it was an easy fix.

"It works better when you plug it in." :)
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
Sparky should have known he purchased/installed a fusable disconnect. (Not every ac disconnect is fused.)
Fuse size would only be established once the actual unit was known, so expecting Sparky to put fuses in is unrealistic if the job was scoped out as run a 30A ckt to location X and terminate with a disconnect.

Sparky should have known enough to be able tell Mr. HVAC that he needs to add fuses sized according to nameplate.

This is probably the simplest "problem" anyone could ask for.!! Smile........
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
The electrician should have put fuses in. I have on more than one occasion grabbed a fused disconnect by accident at the box store only to find out I had the wrong thing after I got to the job. Every one of those was returned and replaced with a non fused version.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
Kinda irrelevant since I (homeowner) figured out and fixed the problem but wondering general opinion of the pro's as to who's problem this is/was?

Recently completed garage expansion. As part of it, all new subpanel and everything feeds into that. As part of it, I had the electrician add an outside disconnect and 30 amp 220 circuit to have a split a/c unit installed afterwards. Fast forward a few weeks, hvac friend shows up and installs daikin 24k mini split. And... line side has 240v, no power coming out of the load side of the disconnect. hvac guy talks to electrician, both conclude disconnect is bad, sparky says he will stop by following week to replace it. Never shows....

I pulled the entire thing off the wall, took it apart, no continuity across anything. Google search show me apparently there are supposed to be 2 fuses installed on the back side of the puller. Neither of them ever thought to ask about it when they talked 2 weeks ago...

Is this something the electrician should have added? The hvac guy? Heading to HD to pick up the fuses shortly, just wondering for my own sanity... very disappointed that NEITHER of them thought to check/look and it takes me, a ******* homeowner, to figure out what the problem is.
no the electrician couldnt have added it because he would have no clue what size fuses are needed unless you spec'd the unit when he did the circuit install

that would 100% be on the HVAC co if the AC unit was spec'd later....
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
The electrician should have put fuses in. I have on more than one occasion grabbed a fused disconnect by accident at the box store only to find out I had the wrong thing after I got to the job. Every one of those was returned and replaced with a non fused version.
if the unit was not spec'd when the electrician did the circuit install, how could he know what size fuses were needed?
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,042
Location
Coronado, CA
That is usually done when they do the finish wiring. Since nobody finished it, then I would say the hvac guy that did the finish work should have done it.
The HVAC guy should have tested his work. Had he done so he would have found that the equipment was not working and then put in the necessary fuses.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
if the unit was not spec'd when the electrician did the circuit install, how could he know what size fuses were needed?


The same way I size the breaker when the unit isn't there yet. By calling the mechanical contractor and asking. What if it was a non fused disconnect? How would he know what size breaker to use?

The HVAC contractor knows what they are going to install.
 
OP
T

tfalk

Well-known member
Joined
Mar 30, 2015
Messages
319
Location
Somerset NJ
no the electrician couldnt have added it because he would have no clue what size fuses are needed unless you spec'd the unit when he did the circuit install
Electrician WAS given specs for unit when wiring was installed, appropriate 220/30 breaker and disconnect were installed. They just never installed the fuses needed for the disconnect to actually work.
@nadogail HVAC guy is the one who found out the disconnect had no power to the load side when he installed the split. He spoke to the electrician who installed the disconnect and they jointly decided the disconnect was bad. Apparently neither thought to ask if either had installed the fuses needed.

Problem is resolved, I bought the fuses and installed them and the unit works fine. I was just trying to see what the consensus would be among trades people who should have installed the fuses rather than me having to find and resolve the problem.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
Electrician WAS given specs for unit when wiring was installed, appropriate 220/30 breaker and disconnect were installed. They just never installed the fuses needed for the disconnect to actually work.


Telling him to install a 30 amp 240 volt AC circuit is generic but common. I doubt the unit needs 30 amps. I've personally never seen a mini split that needed more than 20 amps. Everything for sizing the wires and fuses is on the nameplate. That is where the "he didn't know what size fuses to install" is coming from.
 
To avoid these ads, REGISTER NOW!

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
HVAC guy installed unit. Who spec’d the unit?
I do see this as part of the hvac install. Confirming I have power present at my incoming disconnect is a priority. If it ain’t there, now is the time to fix it. HVAC guy should have looked deeper into it. He was on-site.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
The same way I size the breaker when the unit isn't there yet. By calling the mechanical contractor and asking. What if it was a non fused disconnect? How would he know what size breaker to use?

The HVAC contractor knows what they are going to install.

You're lucky if you get an actual answer. Most of the time when I ask that they don't know the electrical specs, "It's a 2 ton".
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
You're lucky if you get an actual answer. Most of the time when I ask that they don't know the electrical specs, "It's a 2 ton".
I've been given the two ton answer many a time, but It's worth a shot because I don't want to go back over something stupid like changing a breaker from a 230 to a 225.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
I am not in either of these trades but I believe the "normal" install is a disconnect, not a fused disconnect, so if something was installed out of the expected norm I would at least expect a note in the box. I would be much more concerned about the lack of integrity of a person that says he will show up and replace a suspected failed unit yet is a total "no show".
 

BrandonV

Well-known member
Joined
Jun 9, 2023
Messages
4,030
Location
Arizona
The last time I installed a mini-split the only disconnect available at the hardware store came preinstalled with fuses too big for the nameplate max fuse/MOP.

Are you sure someone didn't pop them out to replace them at a later point with the correct size fuses but forgot?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
I've been given the two ton answer many a time, but It's worth a shot because I don't want to go back over something stupid like changing a breaker from a 230 to a 225.
In that case, the fused disconnect disconnect puts the burden of final fuse sizing on Mr. HVAC and the "oversized" cb in the panel can stay as is - no return trip needed. CB is then only protecting the conductors from short circuit.

Verifiying the proper circuit protection is all part of commissioning the ac unit. Even if Sparky installed fuses, it still comes back to the person commissioning the unit to verify correct sizing, changing out as required. The cost of a couple fuses isn't worth dealing with chasing this problem back to someone.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
The same way I size the breaker when the unit isn't there yet. By calling the mechanical contractor and asking. What if it was a non fused disconnect? How would he know what size breaker to use?

The HVAC contractor knows what they are going to install.
And what if none of that is decided upon when you install the circuit? Which may have been the case for the OP…
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
I am not in either of these trades but I believe the "normal" install is a disconnect, not a fused disconnect, so if something was installed out of the expected norm I would at least expect a note in the box. I would be much more concerned about the lack of integrity of a person that says he will show up and replace a suspected failed unit yet is a total "no show".
The problem with that is many mini splits actually require fuses
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Kinda irrelevant since I (homeowner) figured out and fixed the problem but wondering general opinion of the pro's as to who's problem this is/was?

Recently completed garage expansion. As part of it, all new subpanel and everything feeds into that. As part of it, I had the electrician add an outside disconnect and 30 amp 220 circuit to have a split a/c unit installed afterwards. Fast forward a few weeks, hvac friend shows up and installs daikin 24k mini split. And... line side has 240v, no power coming out of the load side of the disconnect. hvac guy talks to electrician, both conclude disconnect is bad, sparky says he will stop by following week to replace it. Never shows....

I pulled the entire thing off the wall, took it apart, no continuity across anything. Google search show me apparently there are supposed to be 2 fuses installed on the back side of the puller. Neither of them ever thought to ask about it when they talked 2 weeks ago...

Is this something the electrician should have added? The hvac guy? Heading to HD to pick up the fuses shortly, just wondering for my own sanity... very disappointed that NEITHER of them thought to check/look and it takes me, a ******* homeowner, to figure out what the problem is.
They probably thought it was non fused.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
And what if none of that is decided upon when you install the circuit? Which may have been the case for the OP…
Nobody knows the sizes when I install the circuit, so it will get #10 and a non fused disconnect unless it's for a particularly small space, then it might get #12. It's the trim out stage when I call up the contractor and tell them I need to know. The unit size should be decided by then.
The proper fuse size is no different than the proper breaker size. The electrician here could have very easily made the call to find what he needed when he trimmed it out. If he used a non fused disconnect and ran a 30 amp circuit and the mini split MOCP is 15, is the HVAC tech going to be responsible for changing that out? I doubt he'd even look. Probably just turn the disconnect on and be out of there as soon as the unit started throwing cold air out. If it's permitted, which trade will fail the inspection? (if that even gets looked at). I've had electrical inspectors check to make sure I had the right breaker size, I've also been hired by mechanical contractors to change a breaker because they failed their inspection on a unit change out.

The only time I know the breaker size are the very few times I'm installing the circuit for an old house that never had AC to begin with. That's easy since the unit is sitting on site. In those cases, I won't go unless the condensing unit is there.
 