Kinda irrelevant since I (homeowner) figured out and fixed the problem but wondering general opinion of the pro's as to who's problem this is/was?
Recently completed garage expansion. As part of it, all new subpanel and everything feeds into that. As part of it, I had the electrician add an outside disconnect and 30 amp 220 circuit to have a split a/c unit installed afterwards. Fast forward a few weeks, hvac friend shows up and installs daikin 24k mini split. And... line side has 240v, no power coming out of the load side of the disconnect. hvac guy talks to electrician, both conclude disconnect is bad, sparky says he will stop by following week to replace it. Never shows....
I pulled the entire thing off the wall, took it apart, no continuity across anything. Google search show me apparently there are supposed to be 2 fuses installed on the back side of the puller. Neither of them ever thought to ask about it when they talked 2 weeks ago...
Is this something the electrician should have added? The hvac guy? Heading to HD to pick up the fuses shortly, just wondering for my own sanity... very disappointed that NEITHER of them thought to check/look and it takes me, a ******* homeowner, to figure out what the problem is.
Recently completed garage expansion. As part of it, all new subpanel and everything feeds into that. As part of it, I had the electrician add an outside disconnect and 30 amp 220 circuit to have a split a/c unit installed afterwards. Fast forward a few weeks, hvac friend shows up and installs daikin 24k mini split. And... line side has 240v, no power coming out of the load side of the disconnect. hvac guy talks to electrician, both conclude disconnect is bad, sparky says he will stop by following week to replace it. Never shows....
I pulled the entire thing off the wall, took it apart, no continuity across anything. Google search show me apparently there are supposed to be 2 fuses installed on the back side of the puller. Neither of them ever thought to ask about it when they talked 2 weeks ago...
Is this something the electrician should have added? The hvac guy? Heading to HD to pick up the fuses shortly, just wondering for my own sanity... very disappointed that NEITHER of them thought to check/look and it takes me, a ******* homeowner, to figure out what the problem is.