Why does my compressor keep tripping the circuit breaker?

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
I am getting a bit frustrated now. I have a 33 Gal Craftsman compressor. It is rated for 15 amps. Now I originally had in on a 15 Amp service outlet. It would get to about 90 psi then trip the breaker.

I installed a dedicated 20 amp line (I used the correct wire as well) on a 20 amp circuit breaker with an outlet rated for 20 amps.

Here is the kicker now. It charges air up until it automatically shuts off (125 psi). After it has turned itself off, within about 5 minutes I hear the circuit breaker trip (It was not even trying to pull a load). Mind you this circuit breaker has only 1 electric line going to the outlet. Why does it do this?

Could it be a weak/bad circuit breaker? or could my compressor be trying for more than 20 amps?

I use it on my 20 amp service in my house with an extension cord and it does just fine.



-BWP
 
To avoid these ads, REGISTER NOW!

fatfillup

Well-known member
Joined
Jan 17, 2009
Messages
10,336
Location
Finksburg, Md
Can you amp test the compressor while its running to see what its pulling? Also, how far is the run from the breaker box to the oulet you are having the problem with? You may need to go to heavier wire due to distance. Could be a bad breaker. You could always switch the breaker that it runs on in the house ok to the breaker you are having problems with to test whether its a breaker problem or wire size?distance problem.

Seems odd to me that it trips with no load on. If its pulling the correct amount of amps while its running and your not getting a voltage drop while its running then breaker is suspect.
 

volvo420coupe

Well-known member
Joined
Dec 6, 2008
Messages
598
Location
central Michigan
I've only had problems with my compressor tripping breakers in cold weather on startup. I am interested to hear what caused the problem when you find it.
 
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
Can you amp test the compressor while its running to see what its pulling? Also, how far is the run from the breaker box to the oulet you are having the problem with? You may need to go to heavier wire due to distance. Could be a bad breaker. You could always switch the breaker that it runs on in the house ok to the breaker you are having problems with to test whether its a breaker problem or wire size?distance problem.

Seems odd to me that it trips with no load on. If its pulling the correct amount of amps while its running and your not getting a voltage drop while its running then breaker is suspect.

Good questions.

The wire is less than 15 feet in length from the circuit breaker box.

I ran #10 wire just for overkill.

I am thinking it is the breaker (chinese made box store type).

I also think it is weird it is tripping with no load.

I have a clamp on tester. I will try that... But like you say, why would it work with load, and then fail without one?

-BWP
 
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
you could have a bad plug or outlet

Bought the outlet from Lowe's a week ago... Tried a completely different (and new) one today. Both rated at 20 Amps. Both made in USA. BTW both are not GFCI.

The plug is barely used. In excellent condition. I bought this compressor new.

-BWP
 
Last edited:

Bustawrench

Well-known member
Joined
Dec 29, 2008
Messages
527
Location
South Jersey
Put an ammeter on it and see what's going on.

Is the breaker warm/hot after it trips?

Try swapping the breaker out for another one in the panel, just to see what happens. If the new braker does the same thing, the problem is soomewhere else.
 
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
Put an ammeter on it and see what's going on.

Is the breaker warm/hot after it trips?

Try swapping the breaker out for another one in the panel, just to see what happens. If the new braker does the same thing, the problem is soomewhere else.

The breaker is not hot. (Nor the wires :headscrat)

For less than $4.00 I will go to Lowes and try another breaker. I only have two other breakers that are 20 Amp service which are a completely different brand than the one I bought for this line/service.

Thanks

-BWP
 
Last edited:

Bustawrench

Well-known member
Joined
Dec 29, 2008
Messages
527
Location
South Jersey
The breaker is not hot. (Nor the wires :headscrat)

For less than $4.00 I will go to Lowes and try another breaker. I only have two other breakers that are 20 Amp service which are a completely different brand than the one I bought for this line/service.

Thanks

-BWP

Try to stay with the same brand of breaker as the panel itself.
 
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
I unscrewed the outlet.

circuit2.jpg




Here is a picture of the breaker box. The two breakers I have installed are the two bottom ones. Upon noticing this picture I saw that they were a different 'Type' from the others.

There are type QP and the ones I installed were HOM. Is there a difference?
Perhaps this is an issue?

circuit1.jpg


-BWP
 

Bustawrench

Well-known member
Joined
Dec 29, 2008
Messages
527
Location
South Jersey
Looks like Square D breakers in a Seimens (?) box.........

doesn't look like they really fit to me.........

Only reason I can think of would be poor fit at the buss, causeing the breaker to heat up slowly and trip. Could be current leakage thru the compressor switch to ground, what happens if you unplug the compressor as soon as it shuts off? Does breaker still trip 5 minutes later?
 
To avoid these ads, REGISTER NOW!
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
Looks like Square D breakers in a Seimens (?) box.........

doesn't look like they really fit to me.........

Only reason I can think of would be poor fit at the buss, causeing the breaker to heat up slowly and trip. Could be current leakage thru the compressor switch to ground, what happens if you unplug the compressor as soon as it shuts off? Does breaker still trip 5 minutes later?

They clip in and snap on just fine...... Fit like normal.....


I will try unplugging the compressor and see what happens.

Thanks

-BWP
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Square D Homeline ****. Funny part is how much noise Square D makes about breakers of one brand not being legal to use in a panel of a different brand, even if they fit, yet they came out with the Homeline **** and made it the same as Siemens, Bryant, Murray, GE, etc so it would interchange. They have their own propriety line of panels and breakers, why they felt they needed to introduce the Homeline is beyond me.

Go out and buy a Siemens breaker, at least that is what the rest of yours are (easily spotted by the beveled surface where the ON and OFF lettering is.

Charles
 

Fins/413

Well-known member
Joined
Jan 27, 2009
Messages
161
Make sure your line voltage isn't too high, had that problem years ago and had 135 to 140 VAC. the power company relaced the transformer no more problem.
 

rhandwor

Well-known member
Joined
Oct 10, 2008
Messages
1,366
Check the fit of the plug sometimes non commercial plugs aren't tight enough. Buy a 20 amp plug if it still trips I would try another breaker.
You stated it runs on an extension cord from another 20 amp breaker.
My craftsman compressor can run on 110v or 220v I would suggest hooking it up to 220v
they run better.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
They have their own propriety line of panels and breakers, why they felt they needed to introduce the Homeline is beyond me.
They wanted a line to compete with Challenger, Siemens, etc. It was a brilliant move by the right people, they became the original equipment in a lot of mobile and modular homes now. If you ever need a company turn around hire the guys that come up with that, now a standard stock in most box stores. Excellent business and marketing strategy.
 
OP
B

Blacknwhitepit

Well-known member
Joined
Feb 19, 2005
Messages
3,176
Location
Eastern Tennessee
Check the fit of the plug sometimes non commercial plugs aren't tight enough. Buy a 20 amp plug if it still trips I would try another breaker.
You stated it runs on an extension cord from another 20 amp breaker.
My craftsman compressor can run on 110v or 220v I would suggest hooking it up to 220v
they run better.


I would like to run a 220 line. But, I am out of spaces in my box. I could run an additional panel, but given that I can't make a relatively simple circuit work, I am going to hold off on that.

Anyone know what a Pro costs to run an service panel?

-BWP
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I would change the breaker and if that doesnt work up it to 30A since it is a dedicated wire. I tape off the other side of the duplex and lablel it "air comp only".
 

Attachments

  • chop saw only.JPG
    chop saw only.JPG
    30.3 KB · Views: 25

BetterDays

Well-known member
Joined
Mar 26, 2005
Messages
2,948
Location
Ohio
The compressor may not be 220v compatible. You will definitely want to check that first.
 

rhandwor

Well-known member
Joined
Oct 10, 2008
Messages
1,366
http://www.kerchner.com/electrical/faulty.htm
Look at this and I suggest buying the tester. Home Depot or Lowe's should also have them.
On a home it's easy to make a mistake. All electrical inspectors carry them and check the circuits in a new home. Mine is yellow about 2 inches long and plugs into an outlet. It has small led lights on the end.
 