Will a 240v compressor run without a ground?

dtbingle

Well-known member
Joined
Jun 22, 2016
Messages
216
Location
Michigan
Not saying that anyone should do this, but a couple coworkers and I were debating this.

The original argument was that a neutral line was needed as a return path for current. The counter argument was that my 240v compressor only requires the two hot leads. Each of these leads essentially act as 120v and -120v due to the split phasing to create a 240v potential for the motor. When in operation one lead is the "supply" and the other is the "return", if you're trying to think of current flow. No current should go through ground under normal operating conditions.

So that leads to: 1) Is the above correct? and 2) Do 240v AC compressor motors actually use and need the ground wire as a reference voltage potential? In other words, would the motor still work if the ground was removed?
 
To avoid these ads, REGISTER NOW!

sld961

Well-known member
Joined
Oct 28, 2015
Messages
395
1. Yes, it will still work. 2. No, they don't need the ground. The ground is to return voltage to the panel in case of a short. It is for safety.

Sent from my SM-G930V using Tapatalk
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
Not saying that anyone should do this, but a couple coworkers and I were debating this.

A dedicated 240 circuit doesn't even have a neutral. It DOES have a ground, which is a different wire for fault protection. The motor only has two hot wires and a ground, no neutral.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,892
Location
oregon
No ground needed for NORMAL operation. As said the ground wire is for fault protection.

lg
no neat sig line
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
Not saying that anyone should do this, but a couple coworkers and I were debating this.

The original argument was that a neutral line was needed as a return path for current. The counter argument was that my 240v compressor only requires the two hot leads. Each of these leads essentially act as 120v and -120v due to the split phasing to create a 240v potential for the motor. When in operation one lead is the "supply" and the other is the "return", if you're trying to think of current flow. No current should go through ground under normal operating conditions.

So that leads to: 1) Is the above correct? and 2) Do 240v AC compressor motors actually use and need the ground wire as a reference voltage potential? In other words, would the motor still work if the ground was removed?

Whoever said that needs to take electrical 101.
 

LX-Markham

Well-known member
Joined
Apr 27, 2013
Messages
2,930
Location
Markham, Ont.
^^^exactly.
and did nobody have a smartphone?

Google has ended pretty much EVERY bar argument. Used to be able to "debate" a subject for hours! Now somebody just pulls out a phone and finds the true answer. Argument over. Crickets.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,348
Agree with what others have said but will add that you should ground your compressor not only for path in event of fault but compressed air can also be a source of static electricity. My compressor wiring has ground that goes back to box but I also ran a separate ground wire from the tank directly to cold water pipe as an extra precaution.
 

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
OP: the neutral wire that's commonly seen in homes across US are for appliances that uses both 120v and 240v. Perhaps that's where the confusion.

I would run an induction motor w/o ground, but I wouldn't run it w/o overload protection (built into the motor or on a magnetic starter). If you want to follow code, I'm sure it would recommend you to use ground. BTW, I use ground on my 5hp compressor motor.

I've given you the choice - just pick!
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Regardless of voltage rating or whether a Neutral is used, all alternating current devices are "push-pull". That's why it's called ALTERNATING current :rolleyes:


Tommy
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
No ground needed for NORMAL operation. As said the ground wire is for fault protection.

^^ What he said. I've tested out a few 240v motors with just the hot leads and no ground connected.

Here's a nifty chart if you want to see what 240v looks like, they are essentially 180 degrees out of phase from each other. Ignore the orange & blue lines, that's for 3-phase (high leg delta)...
 

Attachments

  • 3-Phase High Leg Voltages.jpg
    3-Phase High Leg Voltages.jpg
    21 KB · Views: 68

Weird Tolkienish Figure

Well-known member
Joined
Jun 12, 2013
Messages
863
Location
North Shore Boston MA area
^^ What he said. I've tested out a few 240v motors with just the hot leads and no ground connected.

Here's a nifty chart if you want to see what 240v looks like, they are essentially 180 degrees out of phase from each other. Ignore the orange & blue lines, that's for 3-phase (high leg delta)...

I believe this is why a "hanging neutral" can fry 110v electronics devices, without a neutral the hot wires become 220v as they will carry both legs, rather than just one.

I could be wrong of course.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
For the welders, I equate it to MIG.

120v is a push system.

240v is a push-pull system.

AC alternates back and forth 60 times a second.

the voltage doesnt matter.

I believe this is why a "hanging neutral" can fry 110v electronics devices, without a neutral the hot wires become 220v as they will carry both legs, rather than just one.

I could be wrong of course.

Yes thats true for MWBC- multiwire branch circuits. The service drop to houses is a multi-wire branch circuit.
 
To avoid these ads, REGISTER NOW!

forAK

Well-known member
Joined
Nov 11, 2015
Messages
380
Location
Peters Creek AK
So that leads to: 1) Is the above correct? and 2) Do 240v AC compressor motors actually use and need the ground wire as a reference voltage potential? In other words, would the motor still work if the ground was removed?

Yes. No ground is needed be it 120 or 240.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That is really good, I need to study that. I still have trouble with those as I am not a natural electrician. I really don't understand circuits all that well, my skillset is really as a basic installer and with service entrance and simple supply circuits.
 

Advan

Well-known member
Joined
May 25, 2014
Messages
442
Location
Ontario, Canada
There are three wires coming into your house, -120V, 0V, and +120V. if you cross the -120V and +120V lines, you get 240V. If you cross the 0V line with either one of the 120V lines, you only have 120 Volts. Some circuits, like the one for your electric range will include all three wires (plus the ground), because that particular appliance uses both 120 and 240V.
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
For the welders, I equate it to MIG.

120v is a push system.

240v is a push-pull system.

??????????????

It's AC in either case.

What does MIG have to do with this simple question ??

Don't confuse the poor guy.

The Grounding conductor NEVER has ANY current flow, unless there is a fault to Ground.

Like the motor "fries" and power has a path to the housing.

NOT to be confused w a "Grounded conductor", that his compressor does not need.

Need to understand the TOTAL difference between "Grounded",("Neutral") and "Grounding" (connected from frame to Earth, almost always Green color, but sometimes bare uninsulated.)

They ARE the n"same", hooked together at the service dissconect, but then branch off, not be be connected down the line.

Now I'm confusing the guy, TMI.

Dtbingle - You must supply a Ground to the frame of the compressor, OR, IF, it should "Fault to ground", and you lean on it, YOU will highly possibly end up 6' in the dirt Ground.

But no, it does NOT need a Ground or Neutral to work.

Marc
 
Last edited:
OP
D

dtbingle

Well-known member
Joined
Jun 22, 2016
Messages
216
Location
Michigan
Thanks all for the responses and info. For what it's worth, I actually have an EE degree and mainly needed "third-party" responses in the debate to prove my argument of how a 240v motor works :)

An additional part of the debate left out was that he said his compressor has a neutral line and won't run if either the a) neutral, or b) ground was disconnected. I don't remember much about the different types of 240v ac motors, but don't recall if there is any type requiring a neutral. I don't think any would actually NEED a ground to run though - safety concerns aside.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
Thanks all for the responses and info. For what it's worth, I actually have an EE degree and mainly needed "third-party" responses in the debate to prove my argument of how a 240v motor works :)

An additional part of the debate left out was that he said his compressor has a neutral line and won't run if either the a) neutral, or b) ground was disconnected. I don't remember much about the different types of 240v ac motors, but don't recall if there is any type requiring a neutral. I don't think any would actually NEED a ground to run though - safety concerns aside.

A 240v motor wouldn't NEED a neutral because it is 240v

U cant get 240v with a hot and neutral.

This guy either doesnt know what hes talking about and is confused or is pulling your chain.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,026
Location
Coronado, CA
IMHO, your compressor motor will most probably work fine and run a long time with out a Grounded Conductor, commonly referred to as a Neutral.

However, any body who insists you do not need an equipment grounding conductor may well have intentions of consoling your widow in a manner that would be unacceptable to you.
 
Last edited:

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,892
Location
oregon
IMHO, your compressor motor will most probably work fine and run a long time with out a Grounded Conductor, commonly referred to as a Neutral.

However, any body who insists you do not need an equipment grounding conductor may well have intentions of consoling your widow in a manner that would be unacceptable to you.

I'm real curious where YOU connect this Neutral and what color it might be? This is not an area for opinions, if you don't have the training and facts then you should be quietly listening.

lg
no neat sig line
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,061
Location
Modesto, CA
I'm real curious where YOU connect this Neutral and what color it might be? This is not an area for opinions, if you don't have the training and facts then you should be quietly listening.

lg
no neat sig line

Im hoping he was being sarcastic about the neutral. Otherwise i agree with u.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
For the welders, I equate it to MIG.

120v is a push system.

240v is a push-pull system.
Actually it is push push/ pull pull. Rekative to neutral the hots are 180 degrees out of phase. They are pulling in opposite directions. That is how two 120's produce 240.. Then they come towards each other until they hit zero. Repeat as necessary.

Sent from my SM-G900V using Tapatalk
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
IMHO, your compressor motor will most probably work fine and run a long time with out a Grounded Conductor, commonly referred to as a Neutral.

However, any body who insists you do not need an equipment grounding conductor may well have intentions of consoling your widow in a manner that would be unacceptable to you.
That is the point many are making. Neutral and ground are not the same thing, even if they are tied at the service panel. Neutral is a power leg used in 120 volt circuits. Ground is a parh for current that accidentally got out of the insulation to follow rather than passing through you.

Sent from my SM-G900V using Tapatalk
 