Wind kicking out heater

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
1st year i had this heater on very windy days (west wind) it would kick out the heater and cycle. 2nd year i bought the endcap in the picture which is supposed to help, it did, no issues last year. Today the wind is heavy, swirling mostly out of the south and the heater kept cycling. Anything else i can do to help with this wind blowing out the heater issue?
 

Attachments

  • F56CD2E9-8660-46F3-B5A2-7B7FCB505021.jpeg
    F56CD2E9-8660-46F3-B5A2-7B7FCB505021.jpeg
    248.6 KB · Views: 134
  • 71C8EB3C-BFCB-4B38-A3E6-13639FCD8E12.jpeg
    71C8EB3C-BFCB-4B38-A3E6-13639FCD8E12.jpeg
    173.6 KB · Views: 132
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,625
Location
Fargo, ND
You could try a tee instead of the cap.

Going out the roof generally has less issues ove sidewall venting in regards to wind.
 
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
You could try a tee instead of the cap.

Going out the roof generally has less issues ove sidewall venting in regards to wind.

i knew out the side was a risk to this but was easier to do.

if i put a tee at the end instead of the cap, do i leave both ends of the tee open or cap one end? And would having the tee perp or parallel to the ground be better?
 

FMB4

Well-known member
Joined
Jan 19, 2017
Messages
2,926
Yep, through the roof and up past the roof line or below the roof line. Up past is preferred.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,933
Location
Coronado, CA
You have discovered that the easier way to addres a problem is often not the best way to solve it.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,625
Location
Fargo, ND
No, just put a tee on it facing up and down. Leave it open top and bottem. The other posts are complicating things!
It might not make a difference, but it doesn't cost much to try it.
 

58Yeoman

Well-known member
Joined
Oct 1, 2010
Messages
8,999
Location
Central IL
I've got the same heater as you in my 24x40 metal building (75k), and I've got this cap on mine going out the wall. No problems what so ever in about 10 years.vent.jpg
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Agree …….no up over the roof line on the horizontal power vent. TEE end cap will likely work. The TEE can be up and down or horizontal. Mushroom cap might also help.
Typical Instruction:
Horizontal Termination
The Horizontal Termination is used to terminate a horizontal vent system. There are several different Horizontal Termination styles available. These include the Mitered Termination Screen, an Elbow Termination and a Screen Termination. All Horizontal Terminations install the same way by connecting them to the vent pipe via standard Ring & Tab Connection method. The Horizontal Termination must terminate a minimum of 6” from the wall (See Fig. 16 & 17).

17E8F3CA-60E8-4CD2-8BBA-98EAF0372782.jpeg
984165FC-6371-4A82-B018-0F83CE908E5C.png
 

FredWanaker

Well-known member
Joined
Mar 27, 2021
Messages
1,470
Location
NorCal
I am not a heater guy but a thought came to mind. Perhaps the wind gusts are essentially pressurizing and depressurizing the garage, or cross flowing thru that vent. Is the garage properly vented so that pressure differentials on different sides of the house can be equalized thru something other than the heater?
 

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
That is a proper install, you might try terminating it a little closer to the building. It may be that the wind coming over that roof may be affecting it, is the wind coming directly at the wall or from the opposite direction. Also, the above poster may be on to something , next time it happens try leaving a door or window to the outside open a little.
 
Last edited:
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
Thanks for all the ideas. Today wind was coming mostly out of the south which would be directly at the vent. I do have a little room to shorten the termination, i want to make sure i clear the soffit/keep warm exhaust out of attic
 

Attachments

  • DDC7B78A-960C-448B-ACF1-47F3A5BCDF65.jpeg
    DDC7B78A-960C-448B-ACF1-47F3A5BCDF65.jpeg
    275.9 KB · Views: 75

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
If you had the problem with the wind blowing directly at the termination cap I would not expect that shortening it would do any good. My next step would be to try the other style of high wind cap.

 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
Thanks for all the ideas. Today wind was coming mostly out of the south which would be directly at the vent. I do have a little room to shorten the termination, i want to make sure i clear the soffit/keep warm exhaust out of attic
most codes are 18" clearance to the soffit, you will need to shorten the distance to the wall. This should help your problem with the wind getting in. however check your clearance on the install manual and the codes in your area.
 
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
All my venting is duravent. Can i only use duravent or will other type B brands work for the end piece?
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
All my venting is duravent. Can i only use duravent or will other type B brands work for the end piece?
In order to have an approved UL listed system then no,
Duravent also states no to use any other B vent brands "Do not mix and match"
 
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
Would it be any help to put a 90 in then the cap? If i have to stick with duravent i dont see other options for caps.
 

Attachments

  • 42356751-E8D1-407C-B129-3E8AEEE81A55.jpeg
    42356751-E8D1-407C-B129-3E8AEEE81A55.jpeg
    259.9 KB · Views: 60
To avoid these ads, REGISTER NOW!

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
It would be cheaper to build a wind shield out of sheet metal and fab around and fasten with zip screws. or buy a 24" and stick that through and silicone back up and throw cap back on? it looks like you have plenty of space from the soffit, but i could be wrong
 

ripperd

Well-known member
Joined
Jul 2, 2014
Messages
2,044
Location
Twin Cities, MN
Wind is not even necessarily the problem, even if you shield it. The pressure differential of the inside of the garage to the vent outside could be increasing or decreasing the draft.

Another solution is to convert to separated combustion, and have the intake air coming in on the same side near where the exhaust is. Then the pressure differentail is minimal because they are both on the lee or windward side.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
Bring the oulet closer to the wall, then you need a barometric damper
Manuals for garage units that are power vented say NOT to use a barometric damper, if you did use one it has to be installed with safety measures

A13. Do NOT use dampers or other devices in the vent or combustion air pipes. A14. Precautions must be taken to prevent degradation of building materials by flue products. A15. Single wall vent pipe must not pass through any unoccupied attic, inside wall, concealed space, or floor. A16. Uninsulated single wall vent pipe must not be used outdoors for venting appliances in regions where the 99% winter design temperature is below 32°F.
 

FredWanaker

Well-known member
Joined
Mar 27, 2021
Messages
1,470
Location
NorCal
did some quick googling. The cause is likely "back drafting" caused by pressure differential and not wind entering the combustion vent. Threads I could find indicated that horizontal vents are more prone to it because the momentum of the heat rising in the column is not present like in a vertical vent. You can test if it is a back draft by opening a door or window to see if it stops or lessens.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Surprised the pros have not weighed in:

If you look at the instructions B vent is NOT suppose to used in horizontal venting.
B vent may not be the cause of the “kicking out” the heater but it comes in play when swapping termination caps.
B vent in horizontal is subject to corrosion. Mine was a pro install prior to my purchased it rusted away in 5 years. Replaced with CAT III vent a few years back.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
Surprised the pros have not weighed in:
Ouch

E – HORIZONTAL VENTING – RESIDENTIAL 1. For horizontal residential installations these units are certified as Category I appliances. The vent may be single wall material minimum 26 GSG (0.46mm) galvanized steel or equivalent grade stainless steel. Venting A - General Recommendations and Requirements and C - Horizontal Venting General and E - Horizontal Venting - Residential.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
As per the instructions

C – HORIZONTAL VENTING – GENERAL
Due to changes to Z83-8 2009 CSA2.6-2009, the use of single
wall B-Vent is no longer permitted as an acceptable material
when venting horizontally, this change covers both residential
and commercial installations. All horizontally vented units manufactured after July of 2011 must be vented as a CateroryIII Unit/Utility Heater in compliance with UL 1738 & ULS636. Common venting is not allowed when horizontally venting the unit

B – VERTICAL VENTS USING METAL VENT PIPE – COMMERCIAL AND RESIDENTIAL INSTALL ATIONS
MHU compact unit heaters are listed as Category I appliances for vertical vent installations.
1. MHU unit heaters are to be used with NFPA- or ANSI- approved chimneys, U.L. listed type B-1 gas vents, single wall metal pipe, or listed chimney lining system for gas venting where applicable, as well as the modifications and limitations listed in figure 2. Seal single wall vent material according to the section A - General Recommendations and Requirements.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,625
Location
Fargo, ND
I saw it, and wasn't going to say anything. There are hundreds, probably thousands of these heaters installed every day with b-vent. I know, it is wrong, but it is pretty common practice. When I sold equipment at a HVAC supplier we sold ton of b-vent for unit heaters. Most installers did not care. We even had a disclaimer on the ordered that stated "Not for use with horizontal venting on unit heaters"

I didn't mention it because I doubt if he used the proper venting that it would matter for the problem he is having.
 

FredWanaker

Well-known member
Joined
Mar 27, 2021
Messages
1,470
Location
NorCal
so I did notice that the drywall isn't taped. Also noticed all the soffit vents, and that there appears to be no slope in the vent like the manufactures specify on horizontal installations. Hot air rises and does not goes sideways, air can flow thru all the drywall butts from the attic, and air can flow thru the attic with the soffit vents on that side. Who knows how much of a pressure differential is built into this installation, but it is enough to blow out the flame.
 
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
Picture angle, i did put a slope on the vent, 1/4” per foot down for water. Yes i used duravent type b, i know its not code. Before i decided to do it myself i had the vent install quoted by 3 hvac installers, all quoted type b, i know, doesnt make it right. Similar heater in my other garage was installed by an hvac installer, they used type b. Both heaters are power vents that dont get used much.

today, no wind, and worked fine. Im gonna play with the termination end cap. Heater doesnt get used much, i use about 100lbs LP every 2 years.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
As per the instructions

C – HORIZONTAL VENTING – GENERAL
Due to changes to Z83-8 2009 CSA2.6-2009, the use of single
wall B-Vent is no longer permitted as an acceptable material
when venting horizontally, this change covers both residential
and commercial installations. All horizontally vented units manufactured after July of 2011 must be vented as a CateroryIII Unit/Utility Heater in compliance with UL 1738 & ULS636. Common venting is not allowed when horizontally venting the unit

B – VERTICAL VENTS USING METAL VENT PIPE – COMMERCIAL AND RESIDENTIAL INSTALL ATIONS
MHU compact unit heaters are listed as Category I appliances for vertical vent installations.
1. MHU unit heaters are to be used with NFPA- or ANSI- approved chimneys, U.L. listed type B-1 gas vents, single wall metal pipe, or listed chimney lining system for gas venting where applicable, as well as the modifications and limitations listed in figure 2. Seal single wall vent material according to the section A - General Recommendations and Requirements.
I stand corrected, my apologies.
 

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,023
Location
Blacksburg, Va
I can't find it now but..back in the day using wood stoves I 'think' I remember there was some kind of one way flapper for exhaust pipe. It let the exhaust out but would shut if wind tried to blow in toward the heater. Do these exist?
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
I can't find it now but..back in the day using wood stoves I 'think' I remember there was some kind of one way flapper for exhaust pipe. It let the exhaust out but would shut if wind tried to blow in toward the heater. Do these exist?
Its a draft blocker, yes they make them.
 