Wire Clamps Required with Conduit?
nwav8tor
Spokane, WA
I know clamps are required where romex enters a panel or box, but what if you use individual THHN wires in EMT? The EMT gets connected to the panel enclosure or the box, but I don't know if there is a type of clamp you use in such a situation or if it's OK to just leave the wires "loose" since they're enclosed in the EMT. (Can you tell I'm new at this?)
Thanks,
Paul
mrjaw14
Nashville, TN
The NEC has changed their rules for connections to a box where a threaded connector is used.
Basically no you don't need a cable clamp with EMT or rigid going to a junction box or panel, but you can't have exposed threads... if the wire is 4 gauge or larger. they say that a strain on the wire can pierce the insulation on the threads and cause a hazard. Inspectors will want to see the little plastic bushings covering the threads if the wire is over 4 awg. They're so cheap that even though I technically didn't need them on anything except my feeder entrance I used them everywhere
Edit: I know you're probably not using 4 gauge wire, just throwing this out as an FYI
MrMark
Southern Cal.
Really, I thought that was an old rule. I've always tried to do that. It's just common sense to prevent chafing.
foolishpride
Southwestern Ohio
Thanks,
Paul
I'm not real clear what you mean by "clamp". Are you talking about an EMT connector?
Or are you talking about a strap to anchor the conduit?
N
nwav8tor
Spokane, WA
I'm now thinking of using three #2 (or #4 with a residnential exemption) wires for the 100A feeder from the main service panel to the new sub-panel. plus a #8 ground. I'm hoping to put it in 1-1/4" flexible metal conduit for the short run down from the main, through a stud and up into the sub. That should mean a threaded connection at each end. I don't know what the bushings you're talking about look like or how/where they are used.
Thanks,
paul
pattenp
Virginia - USA
Conduit end bushing, this one is for PVC.
This one is for metal....
jeff000
OP, I think you might be in over your head.
No, you can use the PVC on EMT/rigid connectors. No need for a bushing on PVC connectors.
Norcal
If the conductors are #4 and larger, there are no exceptions for PVC.....
N
nwav8tor
Spokane, WA
Conduit end bushings - now I get the picture.
All wiring will be CU...
Not in over my head, but still am planning to have my worked checked by an electrician before I get my final inspection...
Thanks,
Paul