I know clamps are required where romex enters a panel or box, but what if you use individual THHN wires in EMT? The EMT gets connected to the panel enclosure or the box, but I don't know if there is a type of clamp you use in such a situation or if it's OK to just leave the wires "loose" since they're enclosed in the EMT. (Can you tell I'm new at this?)

Thanks,
Paul
 
To avoid these ads, REGISTER NOW!

mrjaw14

Well-known member
Joined
May 22, 2012
Messages
1,958
Location
Nashville, TN
The NEC has changed their rules for connections to a box where a threaded connector is used.

Basically no you don't need a cable clamp with EMT or rigid going to a junction box or panel, but you can't have exposed threads... if the wire is 4 gauge or larger. they say that a strain on the wire can pierce the insulation on the threads and cause a hazard. Inspectors will want to see the little plastic bushings covering the threads if the wire is over 4 awg. They're so cheap that even though I technically didn't need them on anything except my feeder entrance I used them everywhere

Edit: I know you're probably not using 4 gauge wire, just throwing this out as an FYI
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Really, I thought that was an old rule. I've always tried to do that. It's just common sense to prevent chafing.
 

foolishpride

Well-known member
Joined
Mar 21, 2009
Messages
343
Location
Southwestern Ohio
I know clamps are required where romex enters a panel or box, but what if you use individual THHN wires in EMT? The EMT gets connected to the panel enclosure or the box, but I don't know if there is a type of clamp you use in such a situation or if it's OK to just leave the wires "loose" since they're enclosed in the EMT. (Can you tell I'm new at this?)

Thanks,
Paul

I'm not real clear what you mean by "clamp". Are you talking about an EMT connector?

Or are you talking about a strap to anchor the conduit?
 

Attachments

  • EMT-Connector-Set-Screw-Type-.jpg
    EMT-Connector-Set-Screw-Type-.jpg
    28.3 KB · Views: 10
  • d_3840.jpg
    d_3840.jpg
    19 KB · Views: 8
  • minerac00002_20_tn_001.jpg
    minerac00002_20_tn_001.jpg
    5.7 KB · Views: 8
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
The NEC has changed their rules for connections to a box where a threaded connector is used.

Basically no you don't need a cable clamp with EMT or rigid going to a junction box or panel, but you can't have exposed threads... if the wire is 4 gauge or larger. they say that a strain on the wire can pierce the insulation on the threads and cause a hazard. Inspectors will want to see the little plastic bushings covering the threads if the wire is over 4 awg. They're so cheap that even though I technically didn't need them on anything except my feeder entrance I used them everywhere

Edit: I know you're probably not using 4 gauge wire, just throwing this out as an FYI

I'm now thinking of using three #2 (or #4 with a residnential exemption) wires for the 100A feeder from the main service panel to the new sub-panel. plus a #8 ground. I'm hoping to put it in 1-1/4" flexible metal conduit for the short run down from the main, through a stud and up into the sub. That should mean a threaded connection at each end. I don't know what the bushings you're talking about look like or how/where they are used.

Thanks,
paul
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Conduit end bushing, this one is for PVC.

conduit%20bushing.jpg


This one is for metal....

Rigid-Conduit-Bushing.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

jeff000

Well-known member
Joined
May 6, 2012
Messages
437
OP, I think you might be in over your head.


Conduit end bushing, this one is for PVC.

conduit%20bushing.jpg


This one is for metal....

Rigid-Conduit-Bushing.jpg

No, you can use the PVC on EMT/rigid connectors. No need for a bushing on PVC connectors.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
OP, I think you might be in over your head.




No, you can use the PVC on EMT/rigid connectors. No need for a bushing on PVC connectors.

If the conductors are #4 and larger, there are no exceptions for PVC.....
 
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Conduit end bushings - now I get the picture.

All wiring will be CU...

Not in over my head, but still am planning to have my worked checked by an electrician before I get my final inspection...

Thanks,
Paul
 