"wire guard" instead of conduit allowed by code?
ching0n
I have service entrance cables feeding through a cinder wall that I want to protect against nails but don't want to have the meter removed to do so. Are these type of flanged guards allowed? I don't see any "schedule x" rating on them so gut is telling me no but don't feel like welding up a box either. I've got about 4ft of the 3 + ground....so a tight fit is 3"x2"x4' box. Do I need to worry about volume? space is at a premium and framing 2"x3" around it still wouldn't protect against a nail.
Thank you,
edit:
Come to think of it, I guess I could tack and notch a bunch of junction boxes :p
LXCam
Have you thought about 4" X 4" gutter?. It needs to be within a UL listed wireway. Does it need to be weather tight?
C
ching0n
I did think of it but don't like that gutter shape isn't symmetrical. I saw something similar used for HVAC pies that is symmetrical but seemed rather thin. Isn't gutter too thin for the application?
I'm also reading that this type of cable can't be inside the structure either....off gassing or toxic in a fire maybe? Though I'm not sure why it's even called service entrance cable or how it'd connect to the panel otherwise.
LXCam
I get this feeling we’re not talking about the same product
This picture is your typical indoor rated gutter
Jmellc
Durham, NC
That can be buried bare but should be in conduit coming up the wall. Schedule 40 PVC is good, Schedule 80 is better, if subject to physical damage.
C
ching0n
Thanks, learned something new. I think I found a 4x4 wireway "trough" that may work. Would using c-channel or unslotted unistrut channel not be allowed since it's not "UL listed"? It'd probably give me a tighter fit.
mike93lx
Richmond, VA
Some URD is rated for indoor use. What is listed on the jacket? You need to look for rhw-2
If it is just use-2, you need to terminate it outdoors and change to something like SER or thwn/xhhw in conduit