I have service entrance cables feeding through a cinder wall that I want to protect against nails but don't want to have the meter removed to do so. Are these type of flanged guards allowed? I don't see any "schedule x" rating on them so gut is telling me no but don't feel like welding up a box either. I've got about 4ft of the 3 + ground....so a tight fit is 3"x2"x4' box. Do I need to worry about volume? space is at a premium and framing 2"x3" around it still wouldn't protect against a nail.

Thank you,

edit:

Come to think of it, I guess I could tack and notch a bunch of junction boxes :p
 
Last edited:
To avoid these ads, REGISTER NOW!

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,202
Location
AZ
Have you thought about 4" X 4" gutter?. It needs to be within a UL listed wireway. Does it need to be weather tight?
 
OP
C

ching0n

Well-known member
Joined
Jul 21, 2016
Messages
1,496
Have you thought about 4" X 4" gutter?. It needs to be within a UL listed wireway. Does it need to be weather tight?
I did think of it but don't like that gutter shape isn't symmetrical. I saw something similar used for HVAC pies that is symmetrical but seemed rather thin. Isn't gutter too thin for the application?

I'm also reading that this type of cable can't be inside the structure either....off gassing or toxic in a fire maybe? Though I'm not sure why it's even called service entrance cable or how it'd connect to the panel otherwise.
 
Last edited:

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,202
Location
AZ
I did think of it but don't like that gutter shape isn't symmetrical. I saw something similar used for HVAC pies that is symmetrical but seemed rather thin. Isn't gutter too thin for the application?
I get this feeling we’re not talking about the same product

This picture is your typical indoor rated gutter

CFE0E0FD-CAA8-446D-B55D-9F05B7EFC33A.jpeg
 

Jmellc

Well-known member
Joined
Apr 28, 2019
Messages
277
Location
Durham, NC
That can be buried bare but should be in conduit coming up the wall. Schedule 40 PVC is good, Schedule 80 is better, if subject to physical damage.
 
To avoid these ads, REGISTER NOW!
OP
C

ching0n

Well-known member
Joined
Jul 21, 2016
Messages
1,496
I get this feeling we’re not talking about the same product

This picture is your typical indoor rated gutter

CFE0E0FD-CAA8-446D-B55D-9F05B7EFC33A.jpeg
Thanks, learned something new. I think I found a 4x4 wireway "trough" that may work. Would using c-channel or unslotted unistrut channel not be allowed since it's not "UL listed"? It'd probably give me a tighter fit.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,901
Location
Richmond, VA
I'm also reading that this type of cable can't be inside the structure either....off gassing or toxic in a fire maybe? Though I'm not sure why it's even called service entrance cable or how it'd connect to the panel otherwise.
Some URD is rated for indoor use. What is listed on the jacket? You need to look for rhw-2

If it is just use-2, you need to terminate it outdoors and change to something like SER or thwn/xhhw in conduit
 