Vinny
Well-known member
Moved into a new house and I'm trying to route power to a subpanel in the attached garage. I'm putting a 100 amp sub in the garage, but will only be running 60 amps, which is more than I need (all I needed in my last house) for my hobbies and I'd rather just run thinner wire.
I'm going to run 2-2-2-4 aluminum, approximately 100 feet, from the panel into the attic and down into the garage. What I'm unsure about is what kind of wire (SER, THWN, THHN, etc.) I can use in this situation, as the panel is mounted on the outside of the house, and has a conduit going from it up into the attic. See attached picture. It's maybe six or seven feet of conduit before it enters the house.
The conduit already has wire running through it. One set is off a 50 amp breaker for the AC, which comes out of the attic down to the AC outside the house. The other, which I will replace with a 60 amp breaker, is a 30 amp breaker that runs into the attached garage to an unused dryer plug. The conduit is at least an inch thick, maybe an inch and a quarter.
My questions:
I'm going to run 2-2-2-4 aluminum, approximately 100 feet, from the panel into the attic and down into the garage. What I'm unsure about is what kind of wire (SER, THWN, THHN, etc.) I can use in this situation, as the panel is mounted on the outside of the house, and has a conduit going from it up into the attic. See attached picture. It's maybe six or seven feet of conduit before it enters the house.
The conduit already has wire running through it. One set is off a 50 amp breaker for the AC, which comes out of the attic down to the AC outside the house. The other, which I will replace with a 60 amp breaker, is a 30 amp breaker that runs into the attached garage to an unused dryer plug. The conduit is at least an inch thick, maybe an inch and a quarter.
My questions:
- Wire check. For a 60 amp circuit, ~100 feet away, is the 2-2-2-4 aluminum adequate considering voltage drop?
- Because I'm going into conduit, I'm pretty sure I can't use SER wire, which is what the local big box stores sell. Is this true, or is there a relief given for short conduit runs?
- Is it OK to have multiple sets of wire running in the conduit? At least until it gets in the attic?
- If I have to use THWN or THHN wire because it starts off in a conduit, does that mean I'll have to run conduit the entire length of the run (like all the way through the attic?). Currently, the wires running up there are not in conduit, but this house was built in the 50s and I don't know if the owner attempted to do his work to code. It's just Romex wire up in there.