Good evening everyone,
I really need to get this right. Any help appreciated.
I’ve got a conex which will house two 5000VA inverters (Victron) and batteries 200 feet from the shop. Between the two, I have 2” schedule 80 pvc conduit buried at 30 inches. A gentle curve with two 90 degree turns-one at the conex and one at the cabin.
My plan is two inverters for split phase to the cabin.
1. Is it 5000 watts divided by 120 volts? Therefore 41.67 amps per line? The spec sheet for the Quattro says “5000 VA.” Then it de-rates to watts based on temperature. I’m not sure how to translate VA into real world wire size needed.
2. Should I calculate a 3% voltage drop? Or would more conservative be better? 2% or 1%? Loads will be household. Biggest load will be the mini split or small air compressor.
3. I’m guessing aluminum is fine, ok, good enough? Or is copper going to give me some advantage?
4. Line one, line two, neutral, and ground. So 4 wires per the electric FAQ, right? And I’m reading that THWN separate strands is preferable for ease of pulling. Is this the right call? Or is there an advantage to going with 4 conductor direct burial underground feeder even though it will be inside the conduit?
5. What temperature rating should I look for on the wire?
6. The wire size calculator is asking me “raceway, cable, buried in earth, or open air.” I’m not sure which one to pick as I’m using buried conduit.
If I can get these pinned down, I can make a decision on the actual wire.
Happy to provide any other information that may be helpful.
Many thanks

I really need to get this right. Any help appreciated.
I’ve got a conex which will house two 5000VA inverters (Victron) and batteries 200 feet from the shop. Between the two, I have 2” schedule 80 pvc conduit buried at 30 inches. A gentle curve with two 90 degree turns-one at the conex and one at the cabin.
My plan is two inverters for split phase to the cabin.
1. Is it 5000 watts divided by 120 volts? Therefore 41.67 amps per line? The spec sheet for the Quattro says “5000 VA.” Then it de-rates to watts based on temperature. I’m not sure how to translate VA into real world wire size needed.
2. Should I calculate a 3% voltage drop? Or would more conservative be better? 2% or 1%? Loads will be household. Biggest load will be the mini split or small air compressor.
3. I’m guessing aluminum is fine, ok, good enough? Or is copper going to give me some advantage?
4. Line one, line two, neutral, and ground. So 4 wires per the electric FAQ, right? And I’m reading that THWN separate strands is preferable for ease of pulling. Is this the right call? Or is there an advantage to going with 4 conductor direct burial underground feeder even though it will be inside the conduit?
5. What temperature rating should I look for on the wire?
6. The wire size calculator is asking me “raceway, cable, buried in earth, or open air.” I’m not sure which one to pick as I’m using buried conduit.
If I can get these pinned down, I can make a decision on the actual wire.
Happy to provide any other information that may be helpful.
Many thanks