dave*99
Well-known member
Any other important instructions we should know about?It’d be even better with 4 people. And buy more lube than you think you need.
Any other important instructions we should know about?It’d be even better with 4 people. And buy more lube than you think you need.
Agree on a safe wordAny other important instructions we should know about?
Yes. The Victron Quattro.Are your inverters designed to be used together to provide 240? Would be interested to know. I just did some reading about inverter generators and some are designed to be paralleled but that only gets more current at 120, not 240 volts.
Yes, I missed that !Unless I made some mistake 2224 MHF is $1.61/ft and the same in single strands of XHHW totals to $1.37/ft. So just go with single strands.
Not direct bury. It is single strands so it requires conduit everywhere.Yes, I missed that !
Not relevant for OP, but can XHHW be direct buried ? Does it require conduit above ground ?
You can bury EMT?If you put the run in emt, you can skip the ground wire.
Lol. Wrong thread. Was thinking of the 5hp compressor guyYou can bury EMT?
Keep it together man....Lol. Wrong thread. Was thinking of the 5hp compressor guy
Pineapple!He's been too distracted b/c he can't remember the safe word.
Two TwentyHe's been too distracted b/c he can't remember the safe word.
Two twenty.........oneTwo Twenty
Loofah
You can bury EMT?
I'd never, ever do it and I am not aware of anyone that would, but as of the adoption of the 2023 NEC, EMT can be buried as long as the proper fittings are used. I do not know, nor do I care what those fittings are. I took a 2023 update class and this is one of the few things I remember from it.Lol. Wrong thread. Was thinking of the 5hp compressor guy
Redemption!I'd never, ever do it and I am not aware of anyone that would, but as of the adoption of the 2023 NEC, EMT can be buried as long as the proper fittings are used. I do not know, nor do I care what those fittings are. I took a 2023 update class and this is one of the few things I remember from it.
I pulled this off the 'ol interweb since I don't have, and might not ever have a 2023 since we might not be adopting it and if we do, it won't be until late 2025. I'm sure someone on here has a 2023 and can verify it.
2020 Code Language:
358.10 Uses Permitted.
(A) Exposed and Concealed. The use of EMT shall be permitted for both exposed and concealed work for the following:
(1) In concrete, in direct contact with the earth or in areas subject to severe corrosive influences where installed in accordance with 358.10(B)
2023 Code Language:
358.10 Uses Permitted.
(A) Exposed and Concealed. The use of EMT shall be permitted for both exposed and concealed work for the following:
(1) In concrete, in direct contact with the earth, in direct burial applications with fittings identified for direct burial, or in areas subject to severe corrosive influences where installed in accordance with 358.10(B)
I
Yes you are safe!Redemption!